Originally Posted by gfretwell
I see MC there aimed at the 480/277 circuits but nothing for 120/208/240 if you want something other than black/white and adding phases from there.
I think this change in 2011 should have exempted 120v circuits at the branch circuit level, perhaps only for switch legs.
It did not change in 2014
I can understand wanting to identify 480/277 circuits but BOY on the line to line and the purple/gray 277 seemed to do a pretty good job. They should have just codified that.
The only confusion with that is if you had 480 wye and a center tapped 240v delta.
I think that would be so rare that it is not an issue tho.
Workgear for Electricians
triple #214113 10/04/14 12:24 AM
F
Sorry about that last post. I'm having issues with my phone. 😕
triple #214114 10/04/14 12:38 AM
Yes I was speaking of the orange but I meant two services with different voltages.
Of you use it for the 480, it would be confusing as the high leg of the 240.
I really doubt you would see both in one place.
The reality is that you usually only see high leg delta in places where there is a limited need for 3 phase and the PoCo is giving them the cheapest alternative. I have only seen one 240 delta with 3 transformers in 20 years of looking at them.
I assume they grew into it and did not want to rewire their equipment. It is behind the Hogs Breath in Key West and serves a couple customers.
Usually I see a big one for the 120/240 loads and a little one for the high leg.
I guess it might be different in other places.
triple #214115 10/05/14 02:38 PM
I know of no situation with our Pocos where it's actually possible to have 480Y277 service AND 240 center-tapped delta.
Indeed, EUSERC has put the hammer down on 240 center-tapped delta. It's being phased out across the board. Legacy system still exist for older structures, though. Don't get your hopes up if you expect to bid and wire a new installation.
One of the factors that many j-men forget/ ignore is that the neutral for 480Y277 and a derived 208Y120 are 30 degrees out of phase -- with the derived current lagging.
This is noted in every Ugly's -- but its in the fine print.
THIS is the reason why your grays and whites can't get crossed over. You'd end up with an amazing harmonic on the returns.
And, in the same vein, it's a disaster if a hot for BOY is mated to the return for BkRBlu. You'll get wicked harmonics, too.
Those are the conductors that end up getting fried... first.
You might also have your returns undersized, as a result.
In commercial installations, it's my practice to just keep lighting circuits separate from everything else. I isolate them regardless of the Service voltage.
HVAC and lighting are the only loads fed by 480Y277V in commercial practice -- with exceptions for weird equipment, and the elevator system. And those exceptions are really rare.
Industrial is loaded with 480 delta motor loads -- which have largely replaced everything that has come before. With rare exception, I isolate my control circuits. Experience has caused me to shun 480/ 240/ 208 double-pole control relay voltages. They get too much dynamic feed-back from motor EMF.
So, outside of service work, I don't expect to face these troubles.
Tesla
triple #214117 10/06/14 12:28 AM
I think that is how "gray" got to be the defacto 480 neutral color, long before the NEC actually made it legal.
Prior to 2002 we were always arguing whether the gray was "natural" enough to be used for a neutral. wink