ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left

Custom and Personalized Fall Gifts and Decor
Halloween Gifts and Decor

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,055 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Sep 2014
Posts: 2
M
mdelz10 Offline OP
New Member
Guys can you help me to understand the purpose of demand and diversity factors and how to use it in making a load schedule.. thanks in advance ^^

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
Diversity is simply realizing that you probably will not turn on everything you have at the same time (they never met my daughter)
Diversity shows up most in residential calculations. In industrial settings it would not be unusual to compute everything at 100% of it's rating plus the applicable overhead where necessary since it is on when the plant is operating.
Usually we have engineers doing that here on the mainland if this is a big operation.


Greg Fretwell
Joined: Sep 2014
Posts: 2
M
mdelz10 Offline OP
New Member
^^ sir can you teach me to use this diversity and demand factor in residential area. all I know is I need this factors to compute the load schedule, branch circuit, feeder and main service entrance.

Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
It is a little complicated at first. It is usually best to start by looking at a few. Basically you start with the square footage at 3va per sq/ft, apply a correction factor to that and then start adding in the fixed equipment.
There are actually 2 methods you can use.

There are examples in the back of the NEC book but you can also find some work sheets and even a couple Excel templates on the net.

Here are a few examples.

https://www.modestogov.com/forms/pdf/bds_res_electrical-load.pdf

http://www.zenfixit.com/load_calculations.shtml

https://www.mikeholt.com/documents/calculations/formulas/ResidentialLoadCalculations.xls



Greg Fretwell

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5