If there will be both a wall mount oven and a surface unit, I would power them separately. Using a single OCP sounds like a great idea until the family gets invited over for a holiday dinner and supper is cooking on the range at the same time that the cake is baking in the oven.
I would not consider the 2 cooking appliances to be non-coincidental loads.
Even if this works right now for your family situation, what kind of problems are you setting up for whoever eventually buys your house down the road?


Ghost307
Horizontal Ad
Joined: Jun 2004
Posts: 613
S
Member
Here is an example of 2 appliances...

1. GE cooktop model #JP336DDBB ($649) 7.4KW

2. GE single wall oven model #JT3000DFBB ($1399) 4.2KW

Total KW=11.6

Using 220.55 column B along with Note #3 for 2 appliances we can multiply 11.6kw(7.4+4.2) x 65%= 7.54KW

7.54kw / 240volt= 31.42amps

31.42amps is good on a #8wire with a 40amp breaker.

Page 2 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Scott35
Scott35
Moreno Valley, CA. USA
Posts: 2,724
Joined: October 2000
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
550,989 Are you busy
425,630 Re: Forum
396,714 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5