Is it a code violation for put receptacles in a unoccupied spaces? I have air return chase plenums that are accessible but are classified as unoccupied.

Thanks in advance

Dean

Horizontal Ad
Joined: Jul 2004
Posts: 9,998
Likes: 35
G
Member
It has to be in a metal wiring method.
More important is what do you plan to plug in to that receptacle. You can only have equipment "necessary for their direct action upon, or sensing of, the contained air" (300.22(B))and I would want to see the listing. A cord is probably not going to be allowed unless it is plenum rated.



Greg Fretwell
Joined: Apr 2002
Posts: 7,403
Likes: 7
Member
dbravo:
If you proposed a compliant wiring method and what are the receptacles for?

I have seen a compliant receptacle installed for monitoring (testing) equipment use by service techs.


John
Joined: Sep 2013
Posts: 43
Member
I'd think it would be fine .. FAU's up in attic spaces require a power source which are not meant to be use by any occupant .. as long as the power source is readily accessible for maintenance or service and conform to other necessary NEC guidelines as far as approved boxes,fittings etc .. really It just can't be buried or covered up.


Anyone claiming to know everything about Electrical, is wrong.
Joined: Jul 2004
Posts: 9,998
Likes: 35
G
Member
"Unoccupied space" is not an issue in the NEC. They only address the physical concerns (environmental air handling space, damp/wet location, hazardous location etc).


Greg Fretwell
Joined: Mar 2013
Posts: 46
Member
"Rules" in this area are a bit fuzzy. Receptacles are "not permitted" in areas like the space above a suspended or drop ceiling, and yet, there are devices (condensate pumps etc) that are plug-in as OE, and they sometimes have to go into these spaces.

To answer the OP's question literally and directly, though, it is no code violation to put ANYTHING in an "unoccupied" space. As soon as the last person leaves a room... it becomes an "unoccupied space". wink

Last edited by NickD; 10/07/13 10:47 PM.

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
331,588 Are you busy
256,804 Re: Forum
238,649 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5