I consider the addition of a requirement that all circuits sharing a neutral be grouped together and be on a common-trip breaker to be a restriction on the use of multi-wire circuits.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
Type 1 & 2 are basically construction materials in load bearing walls and floors that re non-combustible (no wood)

This is a link to the IBC referenced Florida Building Code

http://ecodes.cyberregs.com/cgi-exe...nonindx/ST/fl/st/b200v10/index.htm#b=603


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Reno:
FRom the '11 NEC....."(D) Grouping. The ungrounded and grounded circuit conductors of each multiwire branch circuit shall be grouped by cable ties or similar means in at least one location within the panelboard or other point of origination.
Exception: The requirement for grouping shall not apply if
the circuit enters from a cable or raceway unique to the
circuit that makes the grouping obvious."

Now, with the exception, some opinions are that a xx/3 NM qualifies for the exception. Or, one tye-wrap per MWBC is not that big of a deal is it??



John
Joined: Jan 2005
Posts: 5,485
Likes: 4
Cat Servant
Member
You're also required to land them on a a common-trip breaker -though a handle tie will suffice. No more landing the wires on whatever spaces might be handy; they have to be next to each other.

Big deal? I don't have a problem with the idea, though whether it should be a matter of code is another discussion, for another thread.

It's still a restriction, however small.

Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
The exception clearly says if the conductors of the MWBC come in on a single cable they are "grouped".

Quote
Exception: The requirement for grouping shall not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious.


As for the paired breakers, it sounds more reasonable than a lot of new code rules we have seen. I always wondered why this wasn't a code rule. It certainly avoids confusion a few years down the road.
These are both things conscientious electricians have always done.