Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Thanks Yooper
I knew I was missing something but I just could not find it.
This is at the end of 215.2(A)(1)

Quote
The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel.


This came in 2005


Greg Fretwell
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Oct 2002
Posts: 830
S
Member
So if it cannot be smaller than the equipment ground required according to table 250.122, for a 125 amp breaker the minimum neutral would be #6 copper or #4 aluminum.

Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
At this point you might want to consider not running a neutral at all and running a separate circuit for that one 120v load.


Greg Fretwell