a have a dumb question...Can you run liquid tight flex through stucco? One of our technicians install a light fixture but ran LT flex through stucco and itsonly about 8 inches.I was trying to find something in the code book.
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Sealtite is only suitable for above ground and direct burial installations.
It says so right on the material.
Tesla
|
|
|
|
|
Joined: Jul 2004
Posts: 10,049 Likes: 38
Member
|
Why not? 356.10 Uses Permitted. (7) For encasement in concrete where listed for direct burial and installed in compliance with 356.42.
Not really relevant but ...
356.42 Couplings and Connectors. Only fittings listed for use with LFNC shall be used. Angle connectors shall not be used for concealed raceway installations. Straight LFNC fittings are permitted for direct burial or encasement in concrete. They usually use smurf here if it can be called interior (like the back of a pancake) but I see LFNC if there is a question.
Greg Fretwell
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Stucco/concrete debate coming soon??
I see no issue with the LFMC or the LFNC as long as the connectors are straight.
John
|
|
|
|
|
Joined: Jul 2004
Posts: 10,049 Likes: 38
Member
|
Stucco is basically concrete without the gravel. Any concerns with damage to the wiring method is the same.
Greg Fretwell
|
|
|
|
|
Joined: Jan 2005
Posts: 5,485 Likes: 5
Cat Servant Member
|
I've tried very hard for the past day, and I cannot think of any location that is not either above ground or in the ground.
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Possibly...a 'Black Hole', or another dimension??
John
|
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
 Underwater isn't above ground or direct burial??
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
I posted about Sealtite because I'm constantly running into journeymen, foremen and contractors who are unaware that it's appropriate for most applications -- particularly to include direct burial.
As electure correctly notes, it's not for use in the ocean -- nor is it NASA rated.
Like MI, it's big fault is that it's not cheap.
BTW, angled fittings are not acceptable in buried work. That would also include encased work, too.
Tesla
|
|
|
|
|
Joined: Nov 2002
Posts: 244
Member
|
Speaking of angled fittings. I made an instinctive call last week on a job. I saw an angle fitting installed in the back of a box. The fitting would be in the wall so I said " Hey! you can't use that fitting like that in the wall". Only problem was that it was MC cable. DER.....
|
|
|
Posts: 2,724
Joined: October 2000
|
|
|
|
|
|