harold endean #209107 03/07/13 10:43 AM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Shortcircuit:
Yes, modifications to buss cause issues with the listing. Alas, it has been 'common practice' for some time.

Dependent on having a PE/EE provide methods and materials, and a signed sealed drawing, it is acceptable in most cases.

A few jobs required the mfg to provide the materials and make the mods, and provide UL field certification. That is when $$$ is no object, as it it very costly


John
Work Gear for Electricians and the Trades

Workgear for Electricians

harold endean #209250 03/19/13 12:23 AM
Joined: Jun 2004
Posts: 613
S
Member
bump Harold, how did this job work out?

harold endean #209303 03/23/13 11:52 AM
Joined: Feb 2002
Posts: 2,233
H
Member
I went back yesterday. I had a new set of drawings that showed the correct way it was all actually installed. There were some 800 amp quick blow fuses before the tap for the PV system. So the feeder to the PV was protected. They also didn't tap the bus, but bugged the incoming wires. II have signed and certified drawings from an EE for this job.

harold endean #209308 03/23/13 12:04 PM
Joined: Jun 2004
Posts: 613
S
Member
Originally Posted by harold endean
I went back yesterday. I had a new set of drawings that showed the correct way it was all actually installed. There were some 800 amp quick blow fuses before the tap for the PV system. So the feeder to the PV was protected. They also didn't tap the bus, but bugged the incoming wires. II have signed and certified drawings from an EE for this job.


Thanks for the follow up Harold.

The EE still has to follow the 120% rule.

harold endean #209752 04/23/13 12:02 PM
Joined: Jun 2004
Posts: 613
S
Member
bumpHow did this work out Harold?

harold endean #209805 04/29/13 01:19 PM
Joined: Feb 2002
Posts: 2,233
H
Member
Short circuit,


The EE did indeed follow the 120% rule and he marked it out on the new set of plans that he drew up.