John, when the lights went out, what you said about the lighting being on an hour bypass vs. manual override is the first thing that popped into my mind. (Hence my original post laugh ) The lighting controls went from "showtime" to "clean up crew" IMO..
News and the word from during the game was an offsite malfunction caused the outage (reclosure picking up a fault?) I smell someone covering their butt!
Tesla.. There's no way this place could operate on a 480V feed from Entergy... I'm guessing at a minimum there's a 12KV feed to an onsite 12KV/4160V sub. From there, going to separate points throughout the stadium and brought down to 480Y/277V and 208Y/120V at individual electrical rooms. Just the size of the place would be a voltage drop nightmare at any less!
lost...
I'm glad you picked up on that.
If the stadium was wired like a casino...
Then the Poco would deliver juice via twin Primary Voltage feeders -- at 12 to 21 kV. Whatever Primary was, it would be directly stepped down to 480Y277. That transform is as common as dust.
Adjacent, dry type, transformers would provide 208Y120 current, very much the minor use of electric power.
The trip occurred at a medium voltage/ Primary Voltage level.
(In the Poco world, medium voltages = 2,000 VAC on up through 35,000 VAC. Depending on the grid, voltages throughout that range are popular as Primary Utility Distribution Voltages.
Long distance power is shunted at high voltages 35kV+ -- very high voltages and so on. I don't work that end of the street. Every time I turn around the classification of these voltages changes.
As a general rule: 1,000 VAC per mile of transit. If the Poco has to shunt current a thousand miles -- they'd like to boost it to 1,000,000 VAC -- even VDC.
No wonder 4160 VAC is so popular within major factories -- and RV parks.)
Tesla
http://www.nola.com/superbowl/index.ssf/2013/02/super_bowl_blackout_could_be_t.html#incart_river
And, now, after all of the above brilliant speculation. ^^^^
"is no longer capable of sustaining the Superdome's maximum electrical demand on just one of the two available medium-voltage electrical feeders."
Tesla
Just wondering do the the utilities have crews on site for major events like this?
And if they do what level would they be staffed at (single trouble man or full line crew), and would they have common parts onsite if required?
Both the old Astrodome and the new Reliant Stadium here in Houston have transmission lines feeding them complete with a substation on site (one for each) Distribution is with multiple HV feeds underground to transformer vaults at the stadium. Reliant Energy (the stadium namesake) used to be the main power co here until deregulation and now only sell power and Centerpoint Energy is the power distribution Co.
I just figured that half the AC SWGR was probably not coordinated.
Hmmmm.....
[Linked Image from electrical-photos.com]
According to http://my.earthlink.net/article/top?guid=20130208/7f691ac0-78a7-483e-b050-eb6062ef98f6
Super Bowl blackout traced to preventive equipment
"An electrical device that had been installed expressly to prevent a power outage caused the Super Bowl blackout, ... Officials of Entergy New Orleans, a subsidiary of New Orleans-based Entergy Corp., said the device, called a relay, had been installed in switching gear to protect the Superdome from a cable failure between the company's incoming power line and lines that run into the stadium....
The switching gear is housed in a building known as "the vault" near the stadium that receives a line directly from a nearby Entergy power substation. Once the line reaches the vault, it splits into two cables that go into the Superdome.... It remains unclear whether the problem with the relay was a design flaw or a manufacturing problem.... "It's not unusual for them to have problems," he said. "They can be unpredictable despite national testing standards recommended by manufacturers."
They updated the story: "Not long after the power company's announcement, the manufacturer, Chicago-based S&C Electric Company, released a statement saying that the power outage occurred because the electric load was too much for the equipment, "exceeding the trip setting for the switchgear relay as set by the system operators."
"Based on the onsite testing, we have determined that if higher settings had been applied, the equipment would not have disconnected the power," said Michael J.S. Edmonds, vice president of strategic solutions for the company.
mbhydro:
I can safely bet that next year when the Superbowl is here in NJ, that there will be POCO on site.
Discussions between our Gov. (Chris Christie) and PSE&G alluded to 'there will be no problems'!! Guarantee, at least a few line crews, a few Underground crews, and a lot of supervision, up to Division VPs will be there.
I have to talk to someone who was on site during the current stadium construction for his input.