0 members (), 1,547 guests, and 8 robots.
#208014 12/19/12 11:07 PM
Break out the pocket protectors and slide rulers for this one. How much CEMF is acceptable in a lighting circuit? I'm trouble shooting a lighting system thats all track lighting. Recently a section burnt up at the coupling and the track, and it supposed a good quality track. Due to its troubled history, I am looking at every angle.
In my research and testing, I discovered a slight unbalance of 0.15 amps via amp clamping all the conductors in the conduit without the grounding couductor.
Is there a way to quantify the resistance of the circuit that is unbalanced? There are two circuits in the conduit with its own grounded conductor. The circuit that the track failed has no measurble CEMF. The second circuit is the one that is reading 0.15 amps. Being that it is in the same conduit as the ciruit that failed, It will affect it some. The big question is is the affect big enough to be concern about?
Any takers onm this one?
sparkyinak #208015 12/20/12 01:02 AM
Gut tells me that you may be overthinking. What I had over many years with track (commercial) was the coupling and/or live end burnouts were results of a poor contact connection.
sparkyinak #208017 12/20/12 02:05 AM
Even though we may look at a manufacturer as being high quality, they're still bound to occasionally throw a weak product out there. The couplings/wiring connectors are usually the weakest link in any track lighting set up. Most track I've come across is rated for 2400w but I've never pushed any near that far... I've seen receptacles that can be snapped into lighting track just like a fixture, leading me to believe the mfrs have quite a bit of faith in the stuff..
Lostazhell #208018 12/20/12 03:53 AM
It's not a case of over thinking. I'm confident in my findings. It's a trivial question at best. I'm addressing every possible angle of failure for a report. There is a long history with this system. If it is not documented, it did not happen. I'm just trying to quantify all my findings for my report.
The question is more about CEMF and its affects and less about the track lighting
sparkyinak #208019 12/20/12 02:29 PM
twh Offline
0.15 is a small amperage. If you are using a clamp meter, it would be tempting to test the accuracy by doubling the loop through the clamp.
If there is a fault to ground, 0.15 amps at 120 volts is about 18 watts. That much heat should be detectable by touch if it all happens at one place. You could try a megger at 250 volts to confirm the problem and pull the lights off the track to eliminate them as a cause.
0.15 amps to ground at 120 volts suggests a ground fault of about 800 ohms, or two faults of about 1600 ohms. It isn't hard to imagine a couple or two with dirt or arcing to be the cause.
I also had problems with track lights that failed at the couplings. It turned out that the ceiling moved when people walked on the second floor.
sparkyinak #208024 12/20/12 11:21 PM
sparkyinak:
I have to agree with what Lost & twh said. I meant no offense to you regarding the 'overthinking'.
HotLine1 #208030 12/21/12 05:27 AM
None taken, john. Just clarify the intent of the OP smile
sparkyinak #208055 12/22/12 09:40 AM
Back EMF I've heard of.
Counter EMF is new to me.
I'd prefer to name it impedance.
Unless you've got ultra special bench test gear -- 0.15A is within the tollerance for error on every piece of field test equipment I've touched.
As for track lighting issues: IMHO they all have touchy joints/ connections.
The actual conductors are thin rails of copper -- sometimes tinned -- but definately not designed for really heavy loads.
Which is to say, that they can mount more loads than their intrinsic bus can carry -- without heating up to a fine glow.
Also, I've run into ancient age resistance style voltage controls/ dimmers that make everything worse -- much worse.
Good luck.
Tesla
Tesla #208058 12/22/12 02:29 PM
Let me rephrase my question. Taking the track light out of the equation, how much CEMF, or back emf is too much to cause problem like wires overheating? For example, there is 5 amps unbalance measured in a circuit. It there a way to calculate the impedance of the circuit based on that 5 amps measured?
Tesla #208060 12/22/12 03:55 PM
twh Offline
Counter EMF, here, is the term used to describe the voltage created by a running motor, which is counter to the applied voltage.