ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Using THWN on automotive circuits
by BigB - 03/22/23 09:46 PM
Continuous load
by HotLine1 - 03/08/23 02:11 PM
How's all our Non-US folks doing?
by dsk - 03/08/23 11:56 AM
Old Computers?
by Bill Addiss - 03/04/23 05:06 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 12 guests, and 48 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#207994 12/16/12 08:53 PM
Joined: Dec 2006
Posts: 33
W
wacked Offline OP
Member
Recently I had an air handler shut down due to a wire rubbed where it goes into the motor. The wire rubbed and arced to ground where it went into the motor and the overload opened the circuit (this destroyed the overload, at 600 Volt!!!) The surprise to me was the fact that the wires are three hots and a bond tie wrapped to the frame of the air handler from the starter/overloads to the motor. Not teck or BX but just three hots and a bond. There are six other air handlers that are wired the same way. The motors have an anti short put into the motor where a connector would thread in. The air handlers are electically certified for Canada but this does not seem proper. Shouldn't these wire be ran in armour or sheathing with proper connectors or???? This particular motor that arced had no anti short installed.

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
That's the way roof top units and furnaces are, too.

Joined: Jun 2006
Posts: 613
M
Member
Wacked.
How the unit is wired is a function of the product approval standard for air handling equipment. This is Part 2 OF the Canadian Electrical code. This is why an inspector looks for an approval label to verify the thing was made to the OTHER electrical code. Ther is a part 3 , 4 and 5 too.

Your work as an electrician is the installation of electrical products which is PART 1 of the CEC and the portion of the code electricians break and inspectors reject or approve.

How the product is wired intenally is not governed by your part 1 installation code. It is regulated by Part 2 which is a lot of code books that govern how the product is made and how it performs as well as the market it is approved for like household and commercial.

Just like the wiring for your range is open inside the stove so may be some of the wiring inside your AH unit.

Joined: Dec 2006
Posts: 33
W
wacked Offline OP
Member
This unit does have an approval label... that still doesn't make it proper due to the fact that there was a failure.
I have looked at other air handlers and teck is used more often than not. Maybe the "other code" for packaged units need to be reviewed.

Joined: Jun 2006
Posts: 613
M
Member
You are saying a manufacturer like engineered air is using teck internally to wire the motors? I don't see that. I built this stuff briefly in an earlier life and we did not use tech or acwu internal wiring. Sometimes we used seal tight. it is very common to see what you describe inside of these air units. The fault is a manufacturers error and I would report that to the Certification Body that approved it. I.E. CSA or cUL. We regulary report product defects to them as they can make the manufacturer fiz the wiring methods used internally.
You cannot judge how a piece of approved equipment is internally wired by comparing it to the code book methods. The code book is about how we wire the parts together the other part of the coed is how the factory makes the products we wire.
Your description of how various factories wire the motors is more related to their designs and what is more important to them withing the part 2 standards.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
BigB 2
triple 2
Popular Topics(Views)
304,960 Are you busy
233,373 Re: Forum
218,105 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5