0 members (), 570 guests, and 18 robots.
Page 2 of 4 1 2 3 4
MarkD123 #207859 12/02/12 09:31 PM
Harold:
Have you considered the morning dew??
MarkD123 #207861 12/02/12 11:17 PM
Maybe I just live in a swamp but I always suspect water first on a GFCI trip problem.
MarkD123 #207862 12/03/12 02:53 PM
Apparently transients on the line side can cause GFIs to trip too, even European RCDs with much higher nominal fault currents. Older 100 and even 300 mA RCDs frequently trip in lightning storms. I'd assume that US GFIs with their much lower trip current are even more susceptible to such phenomena (not necessarily caused by lightning activity).
MarkD123 #207863 12/03/12 02:59 PM
I have not noticed GFCIs tripping here from lightning but I do have a bit of protection on my power.
MarkD123 #207897 12/07/12 12:26 AM
John,
I haven't thought about Morning Dew, but i do drink Mountain Dew on occasions. Actually, I went out there the other day and I wrapped each and every connection with zip lock bags and taped up the ends to keep moister out. The GFI's still trip. I will look into it this weekend. I also bought a bunch of new GFI recp. in case I have to replace. I am wondering if a GFI breaker inside would be better than 5 GFI recpt. out side.
MarkD123 #207898 12/07/12 12:29 AM
Greg,
The last time I had a large lightning strike near me, it took out a large tree, several bulbs and dimmers in the house. I also have a small sub station out behind my property. I also have 8 acres of woods behind me and the sub station. Luckily, it didn't get hit when Sandy hit us.
MarkD123 #207906 12/07/12 05:15 AM
What kind of surge protection do you have?
MarkD123 #207909 12/07/12 11:19 AM
Greg,
NONE as of now.
MarkD123 #207915 12/07/12 01:00 PM
I would get a panel protector at a minimum and take a very good look at your grounding system. Make sure everyone is using it. (telco, cable etc)
MarkD123 #208100 12/26/12 08:39 PM
Have voltage readings been made from G to N / L to N / L to G?
What happens if the GFI Receptacle is pulled out of the box and the ground wire is removed from the receptacle?
Since all of problem pedestals are fed off the same main it seems like the cause is most likely back at the main disconnect.
But then again is could be a mis-wiring at any of the pedestals.
Is the feed to all of the pedestals in conduit the full length? If it’s URD maybe one of the wires are damaged.
Page 2 of 4 1 2 3 4
