Harold:
Have you considered the morning dew??


John
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

MarkD123 #207861 12/02/12 11:17 PM
Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
Maybe I just live in a swamp but I always suspect water first on a GFCI trip problem.


Greg Fretwell
MarkD123 #207862 12/03/12 02:53 PM
Joined: Dec 2001
Posts: 2,518
Likes: 1
T
Member
Apparently transients on the line side can cause GFIs to trip too, even European RCDs with much higher nominal fault currents. Older 100 and even 300 mA RCDs frequently trip in lightning storms. I'd assume that US GFIs with their much lower trip current are even more susceptible to such phenomena (not necessarily caused by lightning activity).

MarkD123 #207863 12/03/12 02:59 PM
Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
I have not noticed GFCIs tripping here from lightning but I do have a bit of protection on my power.


Greg Fretwell
MarkD123 #207897 12/07/12 12:26 AM
Joined: Feb 2002
Posts: 2,233
H
Member
John,


I haven't thought about Morning Dew, but i do drink Mountain Dew on occasions. Actually, I went out there the other day and I wrapped each and every connection with zip lock bags and taped up the ends to keep moister out. The GFI's still trip. I will look into it this weekend. I also bought a bunch of new GFI recp. in case I have to replace. I am wondering if a GFI breaker inside would be better than 5 GFI recpt. out side.

MarkD123 #207898 12/07/12 12:29 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

The last time I had a large lightning strike near me, it took out a large tree, several bulbs and dimmers in the house. I also have a small sub station out behind my property. I also have 8 acres of woods behind me and the sub station. Luckily, it didn't get hit when Sandy hit us.

MarkD123 #207906 12/07/12 05:15 AM
Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
What kind of surge protection do you have?


Greg Fretwell
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

MarkD123 #207909 12/07/12 11:19 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

NONE as of now.

MarkD123 #207915 12/07/12 01:00 PM
Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
I would get a panel protector at a minimum and take a very good look at your grounding system. Make sure everyone is using it. (telco, cable etc)


Greg Fretwell
MarkD123 #208100 12/26/12 08:39 PM
Joined: Jun 2002
Posts: 44
W
Member
Have voltage readings been made from G to N / L to N / L to G?
What happens if the GFI Receptacle is pulled out of the box and the ground wire is removed from the receptacle?
Since all of problem pedestals are fed off the same main it seems like the cause is most likely back at the main disconnect.
But then again is could be a mis-wiring at any of the pedestals.
Is the feed to all of the pedestals in conduit the full length? If it’s URD maybe one of the wires are damaged.