0 members (), 976 guests, and 8 robots.
Page 5 of 5 1 2 3 4 5
Originally Posted by gfretwell
BTW a Home Inspector had no problem with this closet light
You mean that the home inspector had no problem deciding that he needed to add it to his report... Yes? laugh
Workgear for Electricians
It was not on the report at all, nor was this.
[Linked Image from ]
Where was the light fixture manufactured? That might say something.
Reno:
You mentioned...."The irony is that the fixture that started this thread would never be questioned by an inspector, no matter what horrors lay behind the backplate."
If said fixture was flush against the structure surface, NO, I would not be aware of any issue, as we (I) don't remove fixtures upon inspections.
When a luminaire looks 'odd' then I may ask that it be taken off/down for inspection. Your page 1 fixture would not get my attention, unless it was not 'flush'.
As to your shop made energy efficient luminaire, I would not have an issue with it, as long as there was plug connected. I will venture a guess that the cost between the page 1 item, and the 'shop made' is either close, or the shop made cost more. BTW..."nice".
That would still bring up the combustible surface issue in a clapboard, vinyl or T1-11 wall.
Greg:
"That would still bring up the combustible surface issue in a clapboard, vinyl or T1-11 wall."
Clarify, please.
314.25(B)
(B) Exposed Combustible Wall or Ceiling Finish. Where a luminaire canopy or pan is used, any combustible wall or ceiling finish exposed between the edge of the canopy or pan and the outlet box shall be covered with noncombustible material.
I read that to say wires run under the canopy would require that the wall be noncombustible or you need a metal shield.
