Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
hmm.. would this be more appropriate?
heater 2500 / 240 = 10.4 AMPS. x 1.25 for continuous load = 13.
since 15AMP breaker is max 12AMP at 80% load.
Isn't #12 the more correct choice since it can handle up to 16 amp?

btw: I should probably thank you guys for going thru a couple of these with me, and tolerating the side tracking at times.

Last edited by sidmuer; 05/16/12 07:00 PM.
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Sid:

Originally Posted by sidmuer
btw: I should probably thank you guys for going thru a couple of these with me, and tolerating the side tracking at times.


A 'Thanks' would always be appreciated, IMHO.

I'm taking a backseat on CEC.





John
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
No, #12 is wrong.
Originally Posted by sidmuer
heater 2500 / 240 = 10.4 AMPS. x 1.25 for continuous load = 13.
Stop there. That's your minimum circuit ampacity.

Joined: Aug 2002
Posts: 402
J
Member
Originally Posted by sidmuer
hmm.. would this be more appropriate?
heater 2500 / 240 = 10.4 AMPS. x 1.25 for continuous load = 13.
since 15AMP breaker is max 12AMP at 80% load.
Isn't #12 the more correct choice since it can handle up to 16 amp?

btw: I should probably thank you guys for going thru a couple of these with me, and tolerating the side tracking at times.


You did the 80% load thing twice. Once when you did 1.25 x load and then again when you did 80% of breaker.

Joined: Jun 2006
Posts: 613
M
Member
Originally Posted by sidmuer
Ok, if I have 100 AMP panel, in 60 degree ambient temperature, how would I size the wire??

Do I just do 100A x 1.25 for continuous = 125A then Table 5A says at 60 degrees using the middle column wire is .67
so then 125A / .67 = 186.5
So then I go back to table 2 using the middle column wire, I would choose 3 aught? (210AMP rated)

OR:
since 100AMP panel can use #3 rated for 105AMP. I just goto 105AMP / .67 for the 60 degree ambient temp and get: 156.7 = 2 aught (185AMP rated wire from middle column of Table 2 )

OR
is 100amp panels with #3 wire feeders only allowed for residential dwellings, and since it doesn't specify as a residential application/installation for this panel do I stick to the first method?

Thank you.


Method 1 for a commercial
100 / .67 = 149.25 for resi service = 1/0

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Originally Posted by mikesh

Method 1 for a commercial

Method 1? Are you saying that all commercial 100 amp panels, in Victoria, (excluding derating for temperature) are fed with #1 awg?

When you determine the panel size, it might be based on 125% of the load, but the wire size isn't again increased. That would be applying the 125% rule twice. Once for the minimum circuit ampacity and a second time to the conductor.

Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
Thank you. I get it now.
Here is a more interesting one....
I've got 4 x #10tw75 in a 41mm conduit. How many more #16tw75 can I fit into the conduit?
I go to table 9 and I get my max wire size (area in mm) for 41mm conduit in the 40% fill zone.
Then, I goto table 10 to get the area of #16 to calculate my fill, and I see there is no #16. It stops at #14. How can I get the area size of #16 TW75 wire so I may complete the question.?
Or is it a trick question? ie: some rule about having lower than #14 size wire in conduit, and needing some kind of separation?


Originally Posted by jdevlin
Originally Posted by sidmuer
hmm.. would this be more appropriate?
heater 2500 / 240 = 10.4 AMPS. x 1.25 for continuous load = 13.
since 15AMP breaker is max 12AMP at 80% load.
Isn't #12 the more correct choice since it can handle up to 16 amp?

btw: I should probably thank you guys for going thru a couple of these with me, and tolerating the side tracking at times.


You did the 80% load thing twice. Once when you did 1.25 x load and then again when you did 80% of breaker.

Last edited by sidmuer; 05/22/12 07:36 PM.
Joined: Jun 2006
Posts: 613
M
Member
No #3 is still good for a 100 amp panel but feed a 100 amp panel through a 60 degree ambient and derating factors can bump it up a lot.
I think it would be a hugely bad idea to put a panel in a 60 degree ambient as most of the breakers would trip at values musch lower than the number on the breaker.
What would the ampacity be for a 60 degree breaker in a 90 degree ambient? 0 amps

Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
You're right. 60 degree is unreasonable. Even for just a question.
Let me phrase it better....
lets say 200A panel, but lets assume the panel is not in the ambient room, just the supply wires run through somewhere, where it will be 40 degrees ambient. Whats the min size coppers we can use to supply this?
Now, here's my confusion, and it's probably silly. But i need to learn the right way.
So, I would goto Table #2. I see that 210 A is the min rated wire to supply at least 200 A. Which is 3/0. I am not 100%. But I feel I should use this, as it doesn't state that this is a residential property. In which case if it did, I would use 2/0 rated for 185 A which is allowed in homes/individual dwellings.
Now, I feel I need to take that 210 A rated wire and do 1.25 x for continuous load for my panel. Then, I need to factor in the ambience for the wire at 40 degrees. Which is / by .9 using Table 5A.
At this point, I would get: 291.2 A. This leads me to 300Kcmil wire rated at 295 Amps. The issue I have is, that is not one of my multiple choice answer choices. So something is wrong in my way of thinking.
If I use a panel "assumed" (which I don't want to do since it's not stated) for a dwelling, I can choose 185 A. Then, I can just / .9 for ambience and I get 205.6 A which falls into one of my choices.
There are a couple other ways of looking at this. But I'm sure you get the idea, and I don't want to make a winded post. smile
My answer choices are:
1/0, 2/0, 3/0, and 4/0 wire sizing.

Originally Posted by mikesh
No #3 is still good for a 100 amp panel but feed a 100 amp panel through a 60 degree ambient and derating factors can bump it up a lot.
I think it would be a hugely bad idea to put a panel in a 60 degree ambient as most of the breakers would trip at values musch lower than the number on the breaker.
What would the ampacity be for a 60 degree breaker in a 90 degree ambient? 0 amps

Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
bump... ^^^ anybody?