Joined: Mar 2004
Posts: 829
OP
Member
|
In a rehabilitation center does a patient sleeping room become a patient care area once a dialysis machine is introduced?
|
|
|
|
|
Joined: Jul 2004
Posts: 10,056 Likes: 40
Member
|
I would say yes for the receptacle that the machine plugs into.
Greg Fretwell
|
|
|
|
|
Joined: Mar 2004
Posts: 829
OP
Member
|
We ran new bedside circuits with backup power for the machines using hospital wiring methods. The AHJ now wants the lighting to be wired with hospital wiring methods as well. Some of the lighting is existing and some is being added (remodel. We wired the new lighting with regular MC, he wants it changed to hospital grade MC. The original lighting is piped using the emt as the only equipment grounding conductor.
|
|
|
|
|
Joined: Nov 2007
Posts: 764
Member
|
If the fixtures are located more than 7-1/2-feet above the floor and switched from an area outside the patient care are, they don’t need to have the redundant ground so, if that's the case, regular MC should be okay there. As I understand it, if the wall switch is located more than 6-feet away from the edge of the bed, it would generally be considered as outside the patient care area. IMO, 517.13,B exception #2 in the 2011 NEC is improperly worded and misleading. The way it references 517.13,A makes it sound like you have to have the redundant ground, which would make no sense, since it negates the purpose of the exception even being in article.
Do they have permanent fixed water and drain connections for the dialysis unit, like in a clinic? I guess technically the area would become a patient care area, but in the hospitals, those portable hemodialysis units just roll into the room and they run long flexible lines to hook up to the sink faucet for water supply and drain them into the toilet of the patient bathroom. They have all the filtration tanks mounted on the back of the cart. The peritoneal units just look like bags hanging from a pole with a cycler unit and a drain line or bag.
|
|
|
|
|
Joined: Mar 2004
Posts: 829
OP
Member
|
KJay,
There are no water or drain connections, the units are portable and will be wheeled in as needed. Prior to the installation of the bedside circuits for the machines the rooms were only patient sleeping rooms. It looks like the installation of the circuits changed them to patient care areas.
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Did you look at the cord cap on the machine? Green dot??
Greg & Kjay have it 100%
John
|
|
|
|
|
Joined: Jul 2004
Posts: 10,056 Likes: 40
Member
|
I often wondered why they didn't have a different configuration on "hospital" plugs (maybe 4 pin with an extra ground), to help enforce 517 but I bet that would result in an adapter cable.
Greg Fretwell
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Greg: Like the IG pool filter pumps with the factory twistlock?
I came accross quite a few ingenius homeowners this summer up here.
John
|
|
|
|
|
Joined: Jul 2004
Posts: 10,056 Likes: 40
Member
|
I would like to think that in a controlled setting like a health care facility the abuses would be limited but the more I think about it I do wonder why we go to all the trouble to bring a redundant ground to a receptacle and do not continue it to the equipment that actually connects to the patient. The main problem would be getting it implemented. There are probably a million health care facilities and a 100 million pieces of equipment out there. If I was king and able to design the new HCF receptacle it would be a 5-15 with a second ground hole in the middle so it would be backward compatible with old equipment and the new plug getting installed on new equipment. Think of the "stimulus", all of those new receptacles we would have to install. 
Greg Fretwell
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Greg: A small side note to this subject. Our local hospital only 'stocks' HCF devices. Period, that's all they order and have in stock. Office areas, hallways, restrooms, waiting areas, etc. They 'failed' one inspection a few years back for non HCF receptacles in a few new patient rooms, due to what I refer to as 'hurry up fatigue', and were not happy campers. They used to have 'spec' grade in non HCF areas.
Guess the extra $ solves the problem.
John
|
|
|
Posts: 165
Joined: March 2007
|
|
|
|