0 members (), 247 guests, and 14 robots.
#20365 01/13/03 07:51 PM
jdevlin Offline OP
Here is question that was posed today. Can anyone tell if it would violate any code.
A mutli wire circuit with both branches off the same leg using #14 wire and the neutral using #10. Since #10 is rated for 30 amp would there be a code violation.
NOTE:No one is actually trying this is was just a question that was raised.
#20366 01/13/03 07:54 PM
A handle tie on the OCP???
I'm OK with the #10 neutral, and you do have 15 amp OCP on the two hots right??
#20367 01/13/03 07:56 PM
jdevlin Offline OP
Yes 15 amp ocp. The handle tie never came up in the discusion.
#20368 01/13/03 09:19 PM
Do you mean to say both hots on the same phase?
That will make for a strange handle tie.:
#20369 01/13/03 10:05 PM
Iwire:
OK, you're awake. I should have said something like " a tandem/piggyback breaker" with a handle tie.
#20370 01/13/03 10:47 PM
jdevlin...this is one practice that i never liked.i under stand that your running less wire(cost)but if you lose the neutral you could have 240 volts going to a receptacle.
i know they do sell this cable.standard mc cable with a super neutral.but i think it/'s 3#12 and a#10 neutral and a #12 ground for a 3 phase panel .don't no if it comes in #14/w 10 neutral.
i don't see a violation here.15 amp ocp and a #10 neutral.better then the 14/3 used and someone changes the breakers around.
#20371 01/13/03 11:34 PM
If you're on the same leg I don't see the 240V problem with the lost neutral.
In that regard, a tied pair of breakers should be required for code but I've never seen these tied across the same leg. Can you tie your own?
#20372 01/13/03 11:36 PM
I am still confused
jdevlin said
"A mutli wire circuit with both branches off the same leg"
Article 100: Branch Circuit, Multiwire
makes clear that the hots are from different phases
If this is the case all #14s would be fine
But "with both branches off the same leg"
this would not be a multiwire branch circuit, it would be two hots of the same phase coming back on one neutral
the current would add up to potentially 30amps
never seen this done (On purpose) and my reaction would be that it is a violation,
But I do not know how to find it.
lighthouse we do this all the time with 4 wire 3H + 1N + 1G the advantages outway the problems for us.
And for the cables AFC will pretty much get whatever you need.
I just did a job using MC with 3 whites 2 greens 1 each black red blue all #10s Matched up to the office cube furniture
#20373 01/14/03 12:04 AM
Hutch..your right there no way you can get 240 volts on the same circuit.i was just trying to explain this circuit on two seperate circuits breakers.myself i just don't like this practice.
iwire..office cube furniture.3 circuits w/1 isolated ground.receptacles mark a,b,c. nice you can change the receptacles to whatever circuit you like.
#20374 01/14/03 08:11 AM
jdevlin Offline OP
Please not I am not attempting to do this. It was just a discussion that came up as to wether it was a code violation or not IF it was done.
