ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 218 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 3 1 2 3
sparky #202890 09/01/11 03:49 AM
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Greg,

No apologies necessary!
I should have added more details.

Larger Images are so much nicer than small Images!
Small Images are too difficult to view, and are best used for Thumbnails!!! bash

The "2nd" Transformer setup (1st in the latest reply) looks to be a Wye-Wye, with MGCN.
More specific, it appears as 12,470V Primary x 208Y/120 3 Phase 4 Wire Secondary. Apparent Power Rating = 75 KVA (3x 25 KVA)

Per each 25 KVA "Pot" (Transformer):

Primary Split-Coil 7200/12470V Windings setup in Parallel - for 7200 Volts,

Secondary Split-Coil 120/240V Windings also setup in Parallel - for 120 Volts.
(BTW, I have seen only a few Pots where the Center Tap Bushing is used for 120V 2 Wire output - normally the outer Bushings are used only).

The "1st" Transformer Image looks like 7200V x 480Y/277V 3 Phase 4 Wire, Wye-Wye, rated for 150 KVA (3x 50 KVA).

In the areas near me, nearly all Utility Transformer arrays have Delta Primaries (unless the Service is 1 Phase 3 Wire... grin ...).
LADWP had some Open Wye / Open Delta Setups. Saw these in the '70's and '80's.

Wye - or more specific "Grounded" Primaries help stabilize Transient Surges (from Faults, Line Surges and Lightning Surges), help stabilize L-G Voltage (i.e.: Capacitive Coupling Effects) and help stabilize L-G Fault levels.

In addition, Primary Coils have a much lower Voltage across them, which lessens the Flash-over issues between Primary and Secondary sides.

As far as I know, MGCN Systems greatly outnumber Uni-Grounded Common Neutral Systems.

-- Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Work Gear for Electricians and the Trades

Workgear for Electricians

sparky #202891 09/01/11 04:04 AM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Distribution seems to be wye here pretty much everywhere and we have a lot of the 2 transformer "delta Vee" thing. I have a picture of one of those too if you like.
(Mr Bill wants me to resize it before I post it)

We see a bunch of it in the "light industrial bay" type places.



Greg Fretwell
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
Gee,
You guys over there make things so difficult for yourselves.
Over here that would be one single transformer fed with 11 or 22kV (normally single phase).

Trumpy #202905 09/01/11 01:30 PM
Joined: Mar 2011
Posts: 98
V
Member
That's not too bad.

I was on a site walk for a military building two weeks ago that had 3 services (building was only 40k sq ft. One of the services was an 800a, 240v/3p high leg from pole mtd transformers. All three transformers were physically different sizes and A and B were 50kVA while C was 75kVA........

It should be noted that the building was originally an agricultural packing facility.

Last edited by Vindiceptor; 09/01/11 01:38 PM.
sparky #202906 09/01/11 03:44 PM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
Trumpy, I think the PoCos like multiple transformers (of essentially the same type) that they can mix and match in several ways to create all of the strange service arrangements we have. The service truck does not need to carry many different types to fix almost anything.
The 50 KVA unit is becoming the defacto standard around here.
There are several ways to tap them and it has a voltage select switch to enhance that adaptability.

http://gfretwell.com/electrical/Transformer%20connection%20label.jpg


Greg Fretwell
Joined: Oct 2000
Posts: 5,393
S
sparky Offline OP
Member
Quote
Maybe I misunderstand the question but aren't we talking about the grounded conductor on each side of the transformer?

Don't you usually bond all the grounding conductors together?

well, that's what i've been used to doing, but i've been confronted by what is either a demographic electrical standard (from the DC area) , or i've simply been doing it wrong for 2+ decades

so here's the deal>

(you'll please pardon the blue noodle, white or grey wouldn't show up)

I'm used to floating the noodle through on smaller installs, typically 30-50KVA stuff for me

I'm told this isn't correct, and only the creation of a noodle flys



[Linked Image from i104.photobucket.com]

Further, it just seems to me that, if we go the SDS / GEC route, it's not only more work, if it's done repetitively within any given steel structure , i'd been turning the whole place into one big noodle

Quote
This reality is beyond many electricians,
raises hand.....

Last edited by sparky; 09/02/11 09:29 PM.
sparky #202965 09/02/11 09:33 PM
Joined: Oct 2000
Posts: 5,393
S
sparky Offline OP
Member
Quote
Gee,
You guys over there make things so difficult for yourselves.


procrastination is a national passtime here Trump..

~S~

Work Gear for Electricians and the Trades

Workgear for Electricians

sparky #202973 09/03/11 12:26 AM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
If there is no neutral winding on the transformer (AKA wye connected), I wouldn't even bring the neutral there.

I like the bottom connection diagram. We just had this in another thread didn't we?


Greg Fretwell
Joined: Oct 2000
Posts: 5,393
S
sparky Offline OP
Member
Originally Posted by gfretwell
If there is no neutral winding on the transformer (AKA wye connected), I wouldn't even bring the neutral there. ]

I like the bottom connection diagram.


ok, why Greg, and which would be compliant?


Quote
We just had this in another thread didn't we?

sorry if i missed it

~S~

sparky #202979 09/03/11 02:08 PM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
I don't think either are "violations".

This is pretty much your exact question

https://www.electrical-contractor.n...e_to_a_detached_building.html#Post202937


Greg Fretwell
Page 2 of 3 1 2 3

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5