0 members (), 1,035 guests, and 11 robots.
If they are enforcing Class 1 Div 2 you will still need seal offs on the outside and RMC/IMC on the inside. I would ask the AHJ how they want to deal with the penetrations.
Niko Offline OP
I agree that i need seal offs and IMC or RMC inside but if i do conduit on the outside i am eliminating about 90% of the rigid conduit.
I will check with AHJ on sealing requirements.
Thanks all for your replies.
Spray foam.
I bet if you mudded in the pipe with S mortar you could foam in the inside.
Be sure to verify if the putty or caulk you are using is foam friendly.
