Kjay: Good catch. I think Greg meant to type bushing.
Posts: 10,044 Likes: 37
Yup, I got confused myself, I am back to the original opinion I had ... no. For some reason I was thinking about a bonding lock nut with a lug for a jumper. You are right that is a bonding bushing. Now if he had a wedge in there ...
OP
KJay, Yes, that is what I am thinking. I am not sure what Greg is referring to, I am sure he will let me know though!
Originally I was thinking of a regular locking locknut with just a set screw but for some strange reason, later, I got the mistaken idea that the locknut had a lug for a jumper. KJay straightened me out.
In the end, if the concentric ring is the only path for bonding, it is not enough for a service raceway.
OP
Greg,
I went back for final inspection on Wed. and it was changed.