Transformers & Feeders:3Ph 3W Closed Delta 1/2
First Set of Drawings for 3 Phase 3 Wire Closed Delta Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus Primary OCPDs and Panelboards
(Single Voltage SDS, Primary & Secondary OCPD)
NOTE: Click on Image to view Full-Sized Image
Drawing 3PH3W-CD1A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Center Tap Grounded
(Max. Voltage To Ground = 200V, Nominal = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/240.png)
----------------------------------------------------
Drawing 3PH3W-CD2A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Corner Grounded
(Max. Voltage To Ground = 240V, Phase "B" = Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/241.png)
---------------------------------------------------
Drawing 3PH3W-CD3A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Ungrounded
(Max. Voltage To Ground = 0V, no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/242.png)
-------------------------------------------------------------
Text #1: Single Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/214.png)
-------------------------------------------------------------
-------------------------------------------------------------
-------------------------------------------------------------
Transformers & Feeders:3Ph 3W Closed Delta 2/2
Second Set of Drawings for 3 Phase 3 Wire Closed Delta Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus Primary OCPDs and Panelboards
(Single Voltage SDS, Primary OCPD Only)
NOTE: Click on Image to view Full-Sized Image
-----------------------------------------------------
Drawing 3PH3W-CD1B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Center Tap Grounded
(Max. Voltage To Ground = 200V, Nominal = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/237.png)
-----------------------------------------------------
Drawing 3PH3W-CD2B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Corner Grounded
(Max. Voltage To Ground = 240V, Phase "B" = Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/238.png)
-----------------------------------------------------
Drawing 3PH3W-CD3B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Ungrounded
(Max. Voltage To Ground = 0V, no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/239.png)
------------------------------------------------------------
Text #2: Single Voltage SDS - Primary OCPD ONLY
(Click on Image to view Full-Sized Image)
![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/medium/215.png)