#192855 03/07/10 12:42 PM
Joined: Apr 2002
Posts: 203
T
triple Offline OP
Member
Is a 3/8 "romex" connector listed to be used with a combination of a 12-2 and a 14-2 NM running through it? I believe that it has to be two 12-2's or two 14-2's (no mixing of different sized cables allowed). Of course other single cables can also be inserted.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Oct 2006
Posts: 745
E
Member
It depends upon the manufacturer, although I haven't seen any that aren't rated for two identical cables in quite some time.


---Ed---

"But the guy at Home Depot said it would work."
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
A 110.3 (b) issue. Tough argument, unless the packaging happens to bo 'on-site', for either party to 'prove'. (Although the onus is going to be on the EC)

Personally, I haven't came accross this issue for quite a while.


John
Joined: Jul 2004
Posts: 10,044
Likes: 37
G
Member
This is one of those things that if it looks OK it is probably OK. When you see the other listed Romex clamps (buttons and the internal clamps in blue NM boxes etc, these old style connectors look bulletproof. If the jackets all got in there undamaged and they are well secured, what would the problem be?


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Greg:
I was hinting 'discression of the AHJ'. But, basically you don't 'hint'.



John
Joined: Feb 2008
Posts: 165
R
Member
I was always told that part of the connector had to be in contact with the cable thus you were limited to two cables.I have never had an inspector insist that they both be 12 or 14.

Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Originally Posted by Rewire
I was always told that part of the connector had to be in contact with the cable thus you were limited to two cables.I have never had an inspector insist that they both be 12 or 14.


Interesting! Each jacket in contact with the connector, so a stack of three flat cables is NG, but one flat with two 'on edge' may fly?? Something like |=, as oppesed to ||| ?



John
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Nov 2007
Posts: 764
K
Member
You would definitely want to check the connector manufacturers literature.
I know that the Arlington #814, which is a basic two screw 3/8"[1/2"KO] NM connector I often use, is listed for a bunch of different cable combinations, some of which I would not usually consider using, like two 14/2 and one 12/3 in the same connector. I stock some other two-screw connectors made by Topaz that are rated basically the same.

Even the Arlington "black button" plastic 3/8" NM connectors can be used with two 14/3 or two 12/3 cables, and both the T&B and Arlington's plastic push in "wedge lock" style connectors are rated for many different cable combinations as well. These wedge lock connectors are also rated for use with flexible cords within a certain range of diameter.

It gets a little ridiculous with some of the larger size plastic NM connectors, like the 1" and 1-1/4" where they are rated for use with up to nine 14/2 or ten 12/2 as well as several other cable combinations.



Joined: Feb 2002
Posts: 2,233
H
Member
Years ago when I worked with my old boss, we use to install two 14-2 RX wires in one 3/8" connector. Some AHJ's would allow it and others wouldn't. they were never listed for more than 1 wire, but 2 wires would fit in there with no problem. This might be where the AHJ uses 90.4 of the NEC.
There was a proper two wire RX connector which you could install two 14-2 wires,14-3,12-2 or 12-3 wires. The newer plastic connectors ( I believe) are listed for multiple wire connections.

Joined: Feb 2008
Posts: 165
R
Member
Originally Posted by HotLine1
Originally Posted by Rewire
I was always told that part of the connector had to be in contact with the cable thus you were limited to two cables.I have never had an inspector insist that they both be 12 or 14.


Interesting! Each jacket in contact with the connector, so a stack of three flat cables is NG, but one flat with two 'on edge' may fly?? Something like |=, as oppesed to ||| ?

clarify: the side of the cable,not the edge. Now we see why the code is updated every three years

Page 1 of 2 1 2