If you couldn't use straight thread into a conduit body you couldn't use an EMT connector.
I agree jointing RMC is more like plumbing but everything else is a simple, compression, "nut and bolt" situation.
If I had a concern about the "chase nipple/LB" joint it would be that there wasn't a star washer in the joint ... but I have a hard time making a code case unless it was some obscure "paint" reference. A short piece of straight thread with a hard biting lock nut would make me feel better. I look for reasonable fault paths in raceways, even with a green wire. You don't want hot pipe. I know the code really only gets serious in service raceways and fire pumps.


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
In retrospect I bet the tapered thread LBs are listed explosion proof.


Greg Fretwell
Joined: Dec 2000
Posts: 4,294
Member
The tapered threads of some conduit bodies are not intended for use with EMT fittings,chase nipples, or any straight thread fitting, just IMC/RMC, and some are not listed for use as explosion proof fittings.

http://www.appletonelec.com/pdf/A-2-3-4-5-6-15.pdf

http://www.o-zgedney.com/PDF/OZG_AB%5B1%5D.pdf







Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
It is interesting that Appleton starts out saying "Rigid steel, Rigid aluminum IMC and EMT", then drops EMT when they get to the specifics.
How would an inspector know which conduit bodies are listed for EMT?


Greg Fretwell
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Greg, just look at the connectors. If there are lots of threads sticking out of the body, the connector doesn't fit.

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
if it was made up wrench tight the objective of an effective fault path would be met tho. wink