New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 433 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Mar 2003
Posts: 849
Y
Member
No larger then # 6 to Ground rods but to Water lines you must go by 250.66.
250.66 (A) ground Rods
250.66 Table for Water lines.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2007
Posts: 853
L
Member
---250.66 Table for Water lines.--

?? Confused. can't find that.

Joined: Mar 2003
Posts: 849
Y
Member
250.66
States The size of the grounding electrode conductor of a Grounded or ungrounded ac system (SHALL) not be less then given in Table 250.66 (EXCEPT) as permitted in 250.66 (A) though (C).
A = connections to Rod, Pipe, or Plate. # 6 copper
B Concrete cased electrodes # 4 copper
C Ground rings not larger then required by ground ring.
All others must compy with table such as water lines, building steel ect.\

Yoopersup

Joined: Aug 2007
Posts: 853
L
Member
Originally Posted by leland
---250.66 Table for Water lines.--

?? Confused. can't find that.


Still??? AHH now I see what your getting at.

But he has ground rods as primary. Soo..?
I'm missing something.

Last edited by leland; 02/14/09 12:59 AM. Reason: Ahhh etc..
Joined: Mar 2003
Posts: 849
Y
Member
250.50 (ALL) grounding electrodes as described in 250.52(A)1 though (A)6 that are present at each building or structure served (SHALL) be bonded together to form the grounding electrode SYSTEM.
250.52:
A(1) Metal underground Water pipe
(2) Metal frame of the Building
(3) Concrete encaseded Electrode
(4) Ground Ring
(5) Rod and Pipe Elewctrodes
(6) Plate Electrodes
(7) Other metal underground Systems
See examples Soares Grounding book & Nec handbook/