ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 355 guests, and 38 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Feb 2003
Posts: 939
F
Member
Originally Posted by Yoopersup
Revisions on Question.
#1 Load is 7.29 amps on secondary of ist 10 KVA transformer.
# 2 Distance is 3500 ft not 1000 ft as stated before.
Is this enough info ?? also state code sections for answers .
Yoopersup


Okie., we now know the load there from first secondary transfomer load I will readjust the numbers here.,

a shy over kilometer ?? dang that pretty long run ok let me get my chart and try to converted for that distance hope it will cover that range.

Yoopersup.,
Keep in your mind I will slect a common OCPD size so that way you will have a " wiggie " room due the load figures will affect at second transfomer.

I will run a voltage drop caluactions basied on 10 amp @ 480 volts 1Ø{ this size is rather semi common fuse or OCPD size }

#4 CU 4.3%VD {20.5V}
#3 CU 3.4%VD {16.3V}
#2 CU 2.7%VD {12.9V}

Keep in your mind I used 60°C rated conductors.

Merci,Marc



Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2003
Posts: 849
Y
Member
60c Wire rateing>???
In Conduit thhn/thwn???
Also protection & Equipment ground wire size???

Joined: Jan 2004
Posts: 1,507
G
Member
I think I'd use 75° column and probably THWN since it more than likely is a wet location and the over current devices will likely have 75° terminations.

Another thought would be - Could we use a buck/boost transformer?

Very good question Ernie, I've never had to work a problem like that.


George Little
Joined: Jan 2004
Posts: 1,507
G
Member
Additional information-

All conductors on the Primary side of the transformer(s) need to be protected at their ampacity. All conductors on the Secondary of the transformer(s) need to either be connected to an over current device or be protected via the over current device on the Primary side of the transformer and factoring in the turns ratio.
It appears to me that the problem Ernie presented using two transformers would need at the very minimum two over current devices to protect the Primaries of the transformers.

NFPA70 2005 Ed.
240.4, 240.21(C)(1), 450.3(B), Table 450.3(B)


George Little
Joined: Mar 2003
Posts: 849
Y
Member
Wire size due to VD a #2??
Wire size Equipment Ground #6??


Joined: Jan 2005
Posts: 354
P
pdh Offline
Member
At 208 volts, that would be a L-L connection into a 208Y/120 system. I'm wondering how you would be wiring that. Since neither primary connection is grounded, that rules out an autotransformer arrangement. How would the 480 volt secondary be grounded?

Perhaps an even more important question is how will the 208 volt step-down secondary at the far end be grounded? Grounded at one end? Center tapped? it certainly will not have the 120 degree phase angle relative to ground that 208 volts at the origin would have.

Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Yoopersup;

Please excuse me jumping in so late, but I have a couple questions to ask, and a few suggestions.

1: The Transformer at the end of this Loop (Circuit): Will the loads connected only be Line-To-Line 208V 1 Phase 2 Wire, or will there be 120V _AND_ 208V loads?

2: Do the connected loads require 208V 1 Phase 2 Wire, or could 240V 1 Phase 2 Wire be used?

3: Any possibility for 3 Phase loads in the future?

* The 208V 1 Phase 2 Wire Primary may be #6 with 55 Amp 2 Pole breaker.

* The Secondary Conductors may be protected by the Primary OCPD, since there is only ONE (1) derived Voltage from the Transformer's output (480V).

* Suggest to size the complete Circuit per the 10 KVA Transformer capacity.
This would include:
a:) The 480V Transmission Feeders (sized for 21 Amps, and adjusted for the Voltage Drop across 3500 feet of Conductor),
b:) The 208V Primary Feeder (55 Amp OCPD, #6 Feeders, #10 EGC),
c:) The Secondary Feeders at the step-down ("Last") Transformer.

* You might consider Grounding one side of the 480V output on the first Transformer.
This is an option, but for a stable Secondary Voltage to Ground, connecting the Transformer to a GES (Grounding Electrode System) is suggested.

* Suggest to Ground the Secondary of the "Last" Transformer to a local GES.
If the System derived from the "Last" Transformer is to be a "Dual Voltage" (120/240), _DEFINITELY_ Ground the Center Tap of the Transformer to a GES.

I can draw schematics for this scenario if needed.

Lastly, is this an actual proposed installation, or a "What-If" scenario?

Looking forward to your reply.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Mar 2003
Posts: 849
Y
Member
Scott
Yes this is a Actual Installation.
10 kva 208 volt single phase primary 40 amp. OCP at building Secondary 480 volt single phase secondary. 3500ft. run out to a step dn transformer 10 kva .
Loads at second remote transformer 120 volt. So its 120/240 v. single phase.
I feel main not required at second transformer on primary
225.32 Exception #1.
Remote secondary (40)amp OCP required (240.21).then breakers feeding each circuit.
Secondary of remote transformer grounded per 250.30.
Voltage drop on long run requires #2 thwn, Phase conductors
plus equipment ground.
Equipment ground wire 250.122 .
Well a # 6 do it OR is a #2 equipment ground also required per 250.122(B)
10 kva at 480 volts = 20.8 amps
10 kva at 208 volts = 48 amps
load is 5.5 kva at 480 volts = 11.45 amps
load at secondary remote 22.9 amps
Thats what I come out with yer turn .

Yoopersup

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The 208V OCPD can definitely protect the conductors on the 480V side of the transformer, however I do not feel it will be able to be the required 450.3 primary protection for the second transformer.

Joined: Mar 2003
Posts: 849
Y
Member
JBD
According to Transformer section I;d say your probally right,Under Feeder exceptions (No). Thats why I posted it.
Get others opinions .What about the rest of data I posted. Any thoughts there.
Thanks
(Theres a hair line between Pride & stupidy)Right

Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5