Can someone help me out and find in the the NEC2005 where it talks about the location of a disconnect for a sub panel.

Its my unerstaning that you must have not more then 6 disconnecting means for a panel. Does this apply to a sub panel? If so its my undertanding its best to back feed the panel with a breaker and label that as the disconnecting means. OR you can install a fused dissconnect as long as it is "with in sight". Either way the disconneting means must be "with in sight".

I have found the following code referances:230.71 max number of disconnects, and also 230.91 location of OCD. Would these be the correct referances for my situation?

Thannk you as always

E


Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
The 'disconnect' for a sub panel is the circuit breaker/fuses at the source of the feeder for said sub panel.

You must not exceed six (6) switches at the service entrance (excluding exemptions)
ie: a 'main' panel with six (6) switches/brkrs for the feeders/circuits sourced within that panel.

Yes, you can have a 'main' within (or adjacent) to the sub panel, but it is not required.


John
Joined: Jan 2008
Posts: 22
S
Member
As long as the feeding panel, with the CB, it is with in sight that makes sence. But if the feeding panel is not with in sight. I think you must have a CB on the feeders feeding the sub panel.


E


Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Joined: Dec 2000
Posts: 4,294
Member
HotLine1's right

There is no such requirement.

The only things that require a disconnect to be "in sight from " are transformers, motors, fixed heating equipment, storage batteries, tents and concessions, mobile homes, signs, and fixed appliances



Joined: Oct 2000
Posts: 5,393
S
Member
i don't recall a definition of subpanel, methinks that's our own jargon.

that aside, there's much ado about where said 'subpanel' may be.

for instance a 'subpanel' can be withing the same structure, or in a satelitte structure

this becomes, imho, the point of definitional confusion

in the latter case,iirc, although it may be referred to as 'the barn subpanel' it will still fall under the auspices of the 'service entrance' doctrine within the nec...

~S~

Joined: Jan 2008
Posts: 22
S
Member
Originally Posted by sparky
i don't recall a definition of subpanel, methinks that's our own jargon.

that aside, there's much ado about where said 'subpanel' may be.

for instance a 'subpanel' can be withing the same structure, or in a satelitte structure

this becomes, imho, the point of definitional confusion

in the latter case,iirc, although it may be referred to as 'the barn subpanel' it will still fall under the auspices of the 'service entrance' doctrine within the nec...

~S~


So it is correct to say, it must have a single or no more then 6 means of disconnect in it. Or it must have a breaker back feeding the panel for a main.

E


Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified
Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
If the load side panel is in the same structure it does NOT need a local disconnect. If it is in a separate structure there does need to be a disconnecting means in that second building. The 6 throw rule really only applies to "power panelboards". "Lighting and appliance panelboards" (more than 10% of breakers serving branch circuits) can have no more than 2 main breakers. 408.16(A)


Greg Fretwell
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2004
Posts: 1,507
G
Member
Originally Posted by gfretwell
If the load side panel is in the same structure it does NOT need a local disconnect. If it is in a separate structure there does need to be a disconnecting means in that second building. The 6 throw rule really only applies to "power panelboards". "Lighting and appliance panelboards" (more than 10% of breakers serving branch circuits) can have no more than 2 main breakers. 408.16(A)

Greg- look at 225.32 & 225.33


George Little
Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
Hang on there guys...
The OP didn't say anything re: locations, multi-bldgs, etc.

Soko:
A little more detail/info please!!





John
Joined: Jul 2007
Posts: 85
W
Member
unless you're tapping into a set of larger ampacity wires,or bus duct, your sub panel, won't require a breaker. The feeders will be protected by the breaker which feeds them.