ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 118 guests, and 64 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Apr 2002
Posts: 178
R
Member
I`m working with a new contractor whom insist I put a main in the house. I have a 200a meter main out side and have installed a 100 main lug inside with the 100 ocp out in the metermain.Guess I`m not going to find in exact words this is legal I showed him I had ocp for the panel to protect everything has someone got some Code references I can shoot at him.
Wouldn`t 408.36 cover it?

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jul 2007
Posts: 1,337
S
Member
I am not sure what you are shooting at with 408.36. The main is the panel is not required per NEC. I doubt that it is a local ordinance since you are saying it is not required. If the contractor or the customer is going to pay for it, give them what they want. It may just give them a piece of mind. If you have already ordered parts, tell them how much it is going to cost for the change. Check you project specs. if the project came with them.


"Live Awesome!" - Kevin Carosa
Joined: Apr 2003
Posts: 139
B
Member
Yes, 408.36 is the correct section to cite in regard to NOT requiring a "main" breaker inside a panelboard supplied by a feeder with proper overcurrent protection.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Jun 2007
Posts: 301
J
Member
Glad I looked at this thread. I have always understood that a sub panel in an unattached structure requires a main breaker and one or more electrodes, in addition to the main breaker for the feeders.
Is this thread concerning a main service and that is why I do not understand using a lug panel is a violation?
Thanks....john

Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
If you go to a second building you need another disconnect but I understand this as all being in or on the same building. This is not that unusual on a piling house where they have a service disconnect at ground level and a lighting and appliance board up in the dwelling.


Greg Fretwell
Joined: Mar 2005
Posts: 1,213
S
Member
In this case, he's got the OCP/service disconnect as a separate breaker, and so does not need a main breaker on his panel.

Joined: Apr 2002
Posts: 178
R
Member
Yes this is correct. Small cracker box house just set metermain outside to catch the heat and hvac 100 amp sub 20 space in the house. But the main reason for the metermain is the fact of where the panel was located and poco entrance.I coundn`t go back to back.

Work Gear for Electricians and the Trades

Workgear for Electricians


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5