0 members (), 98 guests, and 23 robots.
Just drill a hole and tap a 10-32 and install a ground screw in the plastic.....................................................
Just Kidding I did work for a shop where we had a guy do just this with all the plastic nail on boxes. He spent the whole doing it. He was let go the next day.
Anyway, sounds like a good install to me, unless there is a grounding tail in the fixture for the electronics.
Ob
Workgear for Electricians
As long as the screw was green. smile
I got the idea that the AHJ wanted the armor of the MC bonded per 314.3 and suggested it would work with a bonding bushing as per 314.3 ex2.
heres an update.
I had this inspector out at this location on a different inspection and we got to talk about the MC cable and the exit/emergency light combos. I through out some big words like 'intergrated wiring compartments' and told how it is bonded at the j-box where the MC originated from just a few feet away. All he asked was if the unit was UL listed, and then said it was an 'OK' install.
Not much explination on the original violation other than he was concerned about bonding. I'm kinda thinking he wanted to meet me and let me know who the boss was....
So... MC to a 'intigrated wiring compartment' is a good install.
Shake n Bake
I'm glad the matter was resolved.
I've noticed the lack of a ground wire terminal on exit signs as well. I've also puzzled over the presence of a ground wire terminal on plastic junction boxes.
While some wiring methods always have a ground wire (NM, MC, etc.), you don't always need that ground wire at the end of the run. Exit signs are one such example. I think the boxes have the lug just to give you a place to tie the wire down.
Is this connected to a metal mounting strap? If so, it is to bond steel framing. (a new Florida law)
Ask the inspector if he requires bonding to plastic water pipes too. He must not be very busy to call you on this one.
Or he is just an idiot.
You could have mounted a 4 inch square by 1 1/2 on the surface and ran EMT down to the box and mount the exit on the box.
