0 members (), 167 guests, and 23 robots.
#17285 11/25/02 05:11 PM
ps~ on a steel structure.......
#17286 11/25/02 10:20 PM
Escott,
I would have to say the key issue expressed by everyone [and what I would like to know also] is if there is a Jumper between the existing bus and the new bus.
That would make the Unbalanced Current flow within the Grounded Conductor[s] only - instead of getting to the Grounded Conductor through the Metallic Enclosure.
I know you know this [Ralph Crandom again [Linked Image]...], just added that info to help readers whom may not.
Someone mentioned placing the EGCs on the new bus - which sounds like a good idea too. A Bonding Jumper may still be needed - sized accordingly per highest OCPD of circuits used per the EGCs on that bus.
That's wierd the Factory Supplied Grounded / Grounding Conductors' bus is so limited to available space!
Then again, the amount of Residential work I do is so little, have hardly no clue to what's going on anyway!
Did a Custom House design and install in early 2000, did a Spa last July, and just got a Residential Service relocation / upgrade job last week.
Three Residential jobs in two years [almost three!!!], with maybe 5 between 1995 and 2000 gives me a close to 1 per year rate!
Scott s.e.t.
#17287 11/25/02 10:46 PM
I'm with Hotline on this part
If it's the main panel, with the main disco, then that's where the neutral is bonded to the ground conductors, correct?
If you are adding another termination bar (neutral/ground) the bar you are adding should (IMHO) have a jumper connected to the "factory" bar. The "jumper" should be sized according to the incoming neutral that is connected to the "factory" bar.
and this part
If it's a sub-panel, then there has to be a "ground" bar, and an "isolated" neutral bar, with a "ground" and "neutral" conductor for each.
but I'm not so sure about this part
Gentlemen:
NEC proposal for the number of spaces on a noodle bar?
<Scratching my noodle>,
Doc
[This message has been edited by The Watt Doctor (edited 11-25-2002).]
The Watt Doctor
Altura Cogen
Channelview, TX
