by Hutch - 05/13/24 04:23 PM
Electricians revenge
#124211 09/22/06 01:13 PM
Trumpy Offline OP
Electrictim,
Welcome to ECN, mate!. [Linked Image]
I know this is minor compared to the problem at hand but I don't like the zipties, too tight. Just makes the heating worse.
Not a minor thing at all really.
Perhaps a round tubular spacer under each cable tie (in the middle of the bunch of wires) would aid air circulation?.
Ray,
Is that wire used for the jumpers, that really finely stranded stuff (like welder secondary cable) or ordinary copper cable?.
Just curious. [Linked Image]
[This message has been edited by Trumpy (edited 09-22-2006).]
Trumpy #172155 12/14/07 06:53 PM
Just reading through some of the older threads.
That transformer was upgraded to a 750 kVA, which caught fire on the LV rack about a month ago. ( nov 2007 )
I see if i can find some photo's from that fire.
Now a 1000 kVA TX is installed here.
The silly thing is with this so called de regulation of the electrical industry is feeding these industrial sites via a 185 mm² Al ringmains. The developer puts in the minimum required and problems start almost immediately when the loads builds up in the area.
In the old POCO days, any new supply over 160 Ampères will get an HV supply with a TX on site.
We have had various LV pillars melt down here because of overloading.
Regards, Raymond
RODALCO #172162 12/14/07 09:03 PM
Deregulation is not to blame. Didn't you here? deregulation is a good thing. All kidding aside, professionalism and good work ethics do not require regulation. Greed breeds regulation