1 members (Scott35), 151 guests, and 12 robots.
#167391 08/11/07 02:49 PM
Niko Offline OP
The city electric plan checker needs the following on the plans: DOCUMENTATION REGARDING SERIES BREAKERS :
This was the list that was given to me by the building owner i was not available to ask the plan checker what he meant by series breaker documentation
Can you guys tell me what he means?
Thank you.
Niko #167399 08/11/07 09:05 PM
When you have one breaker used upstream of others, they all must be listed (by UL) for use in series, i.e. the let-through of the upstream breaker is lower than the withstand of the downstream ones. If they are in a panelboard and all are the same make, you should be able to get that info from the manufacturer now. If you have mixed brands within a panelboard or are using stand-alone breakers, you may have to pay a PE to do a certified coordination study on them.
JRaef
jraef #167403 08/11/07 10:26 PM
I'm not sure I understand that explanation.
"Selective co-ordination" is one thing.
I really can't accept the implied requirement that every panel and disconnect be of the same make as the main switchgear.
I think we still need a better explanation of 'series rating,' and when it is relevant.
This might be helpful. Poke around the search box for a few more articles from the magazine
Series rating applies when you are installing a downsteam breaker that has a lower interrupting rating than the available fault current at that point on the circuit. It is the only way you can make that type of installation.
In general a series rating is only obtained by testing. Manufacturer A does not have their breakers tested in combination with other brands. This restriction only applies when you are using a series rating.
Don
Thank you, Don, for straightening out an issue that is confused enough ...
Niko:
What the Plans Examiner is requesting here is for Manufacturer's Spec documents, to be submitted to the Plan Check firm (in hard copy, or "printed" format), which are relavent to a Series Rated System.
These documents will list devices and equipment, that are acceptable to be installed within a Series Rated System. Manufacturer's part numbers + categories will be referenced, as to their use downstream of a given Service Section or Gear Section & OCPD.
If your System IS NOT Series Rated, then write in your reply to the Correction notice:
"This Electrical System Is Fully Rated, Not Series Rated", then submit the marked up correction list to the P/C firm (P/C = Plan Check).
Submit it, along with your contact information + note to have the P/C person contact you for further questions.
If the System is / will be Series Rated, then go to the Manufacturer's website, and printout / download "Cut-Sheets" for their approved combinations of equipment and devices usable on Series Rated Systems.
If you are unsure if the System is / is not Series Rated:
  1. Review the 1 Line Diagram + spec notes of the Planset, look for some indication of Series Rating,
    or,
  2. Verify the On-Site conditions - need to know the Fault Levels at Panelboards, Disconnects, Gear Sections and the Service Equipment.
Maybe there is a high fault level indicated at a remote Panelboard ( > 10KAIC ), which drew attention to the P/C during the exam - and this is why they request the documents.
If this project is Design / Build, and you are the designer, you _should_ know if the System is / will be Series Rated.
I include notes on the cover page, the 1 Line page, and the Panel Schedule page(s) which call out if a System is or is not Series Rated - as follows:
* This System Is a _FULLY RATED_ System (NOT Series Rated).
SCA levels at various points along the system do not exceed the AIR (AIC) of installed Overcurrent Devices or Panels.
or;
* This System Is _SERIES RATED_.
Supporting documents are attached to this Planset, and will be submitted as separate documents - in addition to this Planset - for Plan Examination.
Overcurrent Devices, Panelboards, Service Equipment and other related Equipment intended for use in a Series Rated fashion, have been listed in the Materials Specifications list of this Planset, and have been identified at points on the 1 Line Diagram(s).
Scott
Scott35 #167483 08/13/07 10:30 AM
Niko Offline OP
Thank you gentelman for the detailed explanation.
I learned something today.