ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Any women electricians here?
by HotLine1 - 01/27/22 02:44 PM
12 Lead Motor Connection Weird
by emolatur - 01/19/22 02:40 PM
Well There's your problem.
by gfretwell - 01/08/22 12:17 AM
Happy New Year!!
by HotLine1 - 01/04/22 09:50 AM
Sangamo s309.2
by Robski - 12/31/21 04:54 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 50 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#167319 08/10/07 10:08 AM
Joined: Mar 2005
Posts: 240
Member
are there any code restrictions reguarding bare#6 direct buried. specifically for a sub panel at a detached garage for ground?
also the home owner ran 1/0 aluminum for his feeder, whats the best way now to land in 100 amp breaker split bolt in panel with #2 or j box? in your humble opinions. (obviously cutting strands is a no...no)
thanks,
H20

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
Doesn't that 100a breaker take up to a 2/0 CU/AL?


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Popular Topics(Views)
288,257 Are you busy
220,326 Re: Forum
206,314 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5