Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
Joe Rossi
Work Gear for Electricians and the Trades
Workgear for Electricians
JoeRossi #165996 07/09/07 07:09 PM
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.
See Article 330--especially 330.30