#165311 06/25/07 12:38 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
SOMEONE "BORROWED" MY CODE BOOK OVER THE WEEKEND, CAN SOMEONE GIVE THE 680 REFERANCE FOR THE DISTANCE FROM A JACUZZI THE A DISCONNECT MUST BE--THANKS, CAN'T WAIT FOR JAN. 08 WHEN WE GET TO 2005--FINALLY

Work Gear for Electricians and the Trades

Workgear for Electricians

ccdave #165314 06/25/07 01:36 PM
Joined: May 2005
Posts: 984
Likes: 2
G
Member
Do you mean this one?
680.41 Emergency Switch for Spas and Hot Tubs.
A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings.


Ghost307
ghost307 #165320 06/25/07 04:01 PM
Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
Or this which also applies to a spa
680.22(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.


Greg Fretwell
gfretwell #165329 06/25/07 06:58 PM
Joined: Jun 2005
Posts: 821
S
Member
Don't forget the required GFCI protected receptacle.

ccdave #165356 06/26/07 09:17 AM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
thank you all--dave