0 members (),
98
guests, and
23
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Jan 2005
Posts: 5,485 Likes: 5
OP
Cat Servant Member
|
These pics were provided by Ian, "theelectrickid." I am told that this is a typical GEC arrangement from "Leavitt town" homes of the 60's. First, a bare aluminum wire exits the panel: ![[Linked Image]](https://www.electrical-contractor.net/forum/RS/Leavitton_ECG_1.jpg) Then, under the kitchen sink, the wire terminates at a cold water pipe: ![[Linked Image]](https://www.electrical-contractor.net/forum/RS/Levitton_EGC_2.jpg) As I understand it, there is no ground rod. I have a few issues with this method. Perhaps the first one is suggested by the corroded clamp on the pipe, above the one being used .... aluminum wire + brass connector/ pipe = corrosion. Any thoughts?
|
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
Thanks John. I've seen this done on a few more Levittown homes, mostly when peeking around during an open house. The old, corroded clamp helps the prove this, I'd say. The cold water pipe it connects to goes directly into the slab, then about 20feet to dirt. Only thing you posted wrong was the date, 1950s. Oh, and you spelled 'Levittown' wrong. Ian A.
Is there anyone on board who knows how to fly a plane?
|
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
You might want to double check the solid ground wire to make sure it is aluminum and not tinned copper. It looks as though there is a stranded Cu. wire in the same clamp with the solid. That would be a violation. Each wire needs it's own clamp. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
|
Joined: Oct 2006
Posts: 745
Member
|
We have a community in Northern VA called "Dale City" that was built in the Southern suburbs of Washington, DC in the 1960's. Super cheapo construction and standards; all-gas (even yard lights), all-aluminum wiring, FPE split-bus panels, no central air, (baseboard HW heat), you name it. Yes, there was (and still are) plenty of solid aluminum GEC's.
This community was built to provide "affordable" housing choices in what was then uncharted territory. They cut corners everywhere they could. Nowadays, these home owners are paying the price, big time. The houses may be still be affordable, but the maintenance costs are astronomical. Most of them are now cheap rental properties and have pretty much become ghetto areas.
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
|
|
Joined: Oct 2006
Posts: 745
Member
|
I wanted to add the following:
My first exposure to this was on a "flickering lights" service call. From what I could tell:
1. The neutral in the buried aluminum service drop had failed years ago;
2. The system became reliant upon the GEC as it's neutral;
3. The connection of the GEC to the water pipe or the neutral bus bar failed;
4. The fact that this solid AL GEC merely passed through a "nail hole" in the panel became the neutral. This meant an AL conductor simply touching the edge to the hole in the panel (AL to steel with unintenional contact);
5. This connection arced enough to deteriorate the contact;
6. In the absence of 240 volt loads (again, all-gas homes), any imbalance was carried through this faulty connection;
7. At some point, the "neutral" derrived due to this fault eventually failed, resulting in the flickering lights service call. Years of failed aluminum connections eventually cashed-in.
Does this make any sense? It wasn't the use of aluminum wiring that caused the problem; it was how it was so badly installed.
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Not so much a concern with the old clamp. It's not in use.
Is the clamp that's currently being used in the picture listed for use with aluminum?
|
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
You might want to double check the solid ground wire to make sure it is aluminum and not tinned copper. It looks as though there is a stranded Cu. wire in the same clamp with the solid. That would be a violation. Each wire needs it's own clamp. Alan-- Alan, that's a pure AL wire. (50 years of dust under the sink may tell otherwise though.) Yes there is another wire there, about 18AWG. It disappears into the wall cavity somewhere... Ian A.
Is there anyone on board who knows how to fly a plane?
|
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
Is the clamp that's currently being used in the picture listed for use with aluminum? I peeked under the sink again today (Hi slab!) and looked at. It's for copper only, as noted by a 'CU' marking on it. Ian A.
Last edited by Theelectrikid; 04/14/07 10:20 PM. Reason: Added smiley
Is there anyone on board who knows how to fly a plane?
|
|
|
|
|
Joined: Jan 2005
Posts: 5,485 Likes: 5
OP
Cat Servant Member
|
EVO607797 sent me an E-mail, which, to my great shame, has only now been found by me. He would like to add:
We have a community in Northern VA called "Dale City" that was built in the Southern suburbs of Washington, DC in the 1960's. Super cheapo construction and standards; all-gas (even yard lights), all-aluminum wiring, FPE split-bus panels, no central air, (baseboard HW heat), you name it. Yes, there was (and still are) plenty of solid aluminum GEC's.
This community was built to provide "affordable" housing choices in what was then uncharted territory. They cut corners everywhere they could. Nowadays, these home owners are paying the price, big time. The houses may be still be affordable, but the maintenance costs are astronomical. Most of them are now cheap rental properties and have pretty much become ghetto areas.
|
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
Umm, John/Reno, He posted that about four posts up.  Just pointing that out. Ian A.
Is there anyone on board who knows how to fly a plane?
|
|
|
Posts: 2,724
Joined: October 2000
|
|
|
|