ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 609 guests, and 30 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#15831 10/30/02 10:55 AM
Joined: Nov 2001
Posts: 23
R
rayh78 Offline OP
Member
Have pool pump on 110v with a GFI breaker. Had heard it was cheaper to run as 220v. Is it worth it to rewire? 1 HP motor
Thanks

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#15832 10/30/02 11:28 AM
Joined: Dec 2001
Posts: 50
J
Member
No,it is not worth it. You pay for electriity in watts (power). If you run it at high voltage (240 volts)the amps will drop about in half. But for quick figuring, Volts X Amps = Watts.
So lets say your motor draws 10amps at 120 volts. that is, 10 x 120 = 1200 watts. Now lets say you hook it up to 240 volts and it draws only 5 amps now. That is 5 x 240 = 1200 watts. same thing.
Hope this helps. Have a safe and shockfree time in your pool!

#15833 10/31/02 05:43 PM
Joined: Dec 2001
Posts: 444
S
Member
I was always taught to use the highest voltage rating on a motor nameplate when possible. Power savings (if any) is one reason, but, does the motor not run cooler (less stressed), last longer, and run more efficiently when hooked up 220 vs. 110?

#15834 10/31/02 08:35 PM
Joined: Dec 2001
Posts: 50
J
Member
When the motor is set up for 110 volts the windings are connected parellel. When the motor is connected for 220, the windings are connected in series. Therefore internally on the windings you have the same voltages and current flows on each set of windings.
That's the basic gist of it. I'm not a motor specialist by any means. Perhaps someone with more experiance would like to elaborate.

#15835 10/31/02 08:57 PM
Joined: Jul 2002
Posts: 175
E
Member
Joe is correct. This sketch might help illustrate what he said.

[Linked Image from electric-ed.com]

Ed

#15836 10/31/02 09:03 PM
Joined: Oct 2002
Posts: 210
S
Member
Your motor will not be cheaper to run, but it will run more effeciently at the higher voltage. The higher the voltage the lower the ampacity.

#15837 10/31/02 09:31 PM
Joined: May 2002
Posts: 202
J
Member
As some have already stated lower amps

the key to the higher voltage is you get lower amp draw on a circuit so you can run smaller wire and conduit which reduces cost of install

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#15838 11/01/02 07:40 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Is the start winding on the second drawing supposed to be in series with a run winding?

#15839 11/01/02 12:50 PM
Joined: Jul 2002
Posts: 175
E
Member
Quote
Is the start winding on the second drawing supposed to be in series with a run winding?

Yes, it is. It is a 115 volt winding so has to be in parallel with one half of the run windings (for the high voltage connection).

The two run winding sections in series act as a voltage divider to split the 230 volts into two equal voltages of 115 each.

It will draw it's current through one of the run windings for a few seconds during starting, but that doesn't cause a problem.

All three windings are rated at 115 volts.

Ed
PS - These comments and the diagram refer to the basic general purpose motor. There are many other winding arrangements.

[This message has been edited by electric-ed (edited 11-01-2002).]

#15840 11/01/02 04:21 PM
Joined: Feb 2001
Posts: 89
E
Member
The higher the voltage the less amperage equals smaller wire and OCP.

A little bit of savings I guess.

Page 1 of 2 1 2