Safety at heights?
0 members (), 392 guests, and 30 robots.
#154363 06/08/05 11:59 PM
O
Hi all.
Question for load calculation.
Ive got 2- 50 amp 480 volt 1 ph 70% duty welders.
Using the multiplier .84 for the 70 % duty cycle, I am to use this on the first 2 welders correct?
Also,if using a 3rd welder,using the 85 %,is this 85% of the .84 multiplier.
Your opinions appreciated
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#154364 06/09/05 01:45 AM
That's the way 630.11(B) reads to me
(B) Group of Welders. Conductor ampacity shall be based on the individual currents determined in 630.11(A) as the sum of 100 percent of the two largest welders, plus 85 percent of the third largest welder...
#154365 06/09/05 09:00 AM
I have moved this to the NEC forum. Please post your comments here:
https://www.electrical-contractor.net/ubb/Forum2/HTML/002126.html
Ryan Jackson,
Salt Lake City