141
21
I use Knopp, Square "D", and a Fluke on a daily basis and prefer the Fluke(multimeter) even when I'm busy.
Posts: 8,450 Likes: 4
So, mate, did you actually choose a voltage tester?. What type did you choose? ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
The solenoid testers have the advantage of not measuring "phantom" voltages.
But one big disadvantage, in my opinion, is that they cannot measure hot to ground voltage on GFCI or AFCI protected circuits. The solenoid draws enough current to trip either type of protection.
Steve,
Thats an advantage if you ask me! What better way to test the GFCI?
Steve, What is an AFCI?, is this like an GFCI?, how do they differ? Matt, I don't really like the idea of using a solenoid tester to test a GFCI, as you really need trip times and currents, to make sure that the thing is working properly, I would sooner use a dedicated tester for this. Peoples safety is under-mined if these units are faulty.
Trumpy, AFCI stands for Arc Fault Circuit Interrupter. It "looks" for the characteristics of an arc between hot and neutral. They are required for bedrooms under the latest NEC. An AFCI also provides GFCI protection, but not Class A protection. Class A requires the device to trip at about 5mA of ground current and AFCI's trip at well above 5mA. The SquareD AFCI breaks at 50mA. Still sensitive enough for a solenoid tester to trip it.
I see no problem using a solenoid tester to test a GFCI circuit. When I test a GFCI circuit, my intent is to verify that the wiring is correct - not that the GFCI device meets the manufacturers specs. That is something that I assume their QC takes care of.
Steve: Since we're momentarily on the subject of AFCI's, will it detect an arc in a hot or neutral unto itself, i.e. a loose connection in a plug or a break in a conductor? ...I hope I described that properly... ![[Linked Image]](https://www.electrical-contractor.net/ubb/confused.gif) Mike (mamills) [This message has been edited by mamills (edited 11-07-2002).]