ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left

Custom and Personalized Fall Gifts and Decor
Halloween Gifts and Decor

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,092 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 6 of 9 1 2 3 4 5 6 7 8 9
Joined: Apr 2002
Posts: 2,527
B
Moderator
Heck—no one's opened a can of worms at E-C.net for at least an hour, so here goes...

1) Ever notice that a significant number of manufacturer-furnished weep holes in 3R enclosures are partially or completely plugged by paint?

2) Weep holes have their place in conditions of falling water. Where it’s “hose-directed,” this may often be a misapplication, but that gets into NEMA 4/4X territory.

3} Square D makes an extra-decent {XOP} disconnect switch with a NEMA 12/3 enclosure rating. [This excludes any of that idiotic, dim-witted “12K” crap. That idea’s right up there with ashtrys on motorcycles.] Anyways, their instructions for use as type 3 are/were to drill a couple of (specific-sized) holes in the enclosure bottom plate.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Oct 2000
Posts: 2,749
Member
This subject is growing, and unless I can see, or read some specific words that are truly part of a recognized standard, or code, I will stand behind my comments made here. I thought 110.2 would be that rule.

As I said earlier, I know that the 1/4" hole, or whatever size it is, has been used for many years for the GEC without being bonded to the enclosure, or cabinet.

If that hole is OK for the GEC, then why is there no fitting available that will be capable of being bonded to the enclosure?

The image below shows pieces of a GEC at a service after being hit by lightning. A student brought it to a class for show and tell.

I do have another image that may be helpful but cannot locate it at the moment.

[Linked Image]

[This message has been edited by Joe Tedesco (edited 09-19-2002).]


Joe Tedesco, NEC Consultant
Joined: Nov 2000
Posts: 2,148
R
Member
Joe,
Can you cite any documents that say the 1/4" KOs are the weep holes? Can you cite a rule that says the GEC must use a connector when it enters an enclosure?
Don


Don(resqcapt19)
Joined: May 2001
Posts: 717
G
Member
Joe,
circumstances man!!! Nothing takes a direct strike. No doubt that's some righteous damage.

Joined: Apr 2002
Posts: 558
C
Member
Joe - Even when using a 1/2" K.O. what type of connector are we supposed to use to bond the bare wire to the enclosure? You have shown several types of connectors that are suitable for bonding the armor of armored ground cable but the bare wire is still not bonded until it connects to the neutral buss inside the panel. If the grounding electrode conductor is installed in a raceway it does not get bonded to the enclosure. It may get connected to a grounding bushing on the raceway but this bonds it to the raceway not the enclosure. Is it your opinion that the GEC cold not be installed in PVC since there is no way to bond the wire as it enters the enclosure? I'm not trying to argue with you but if saying the reason that you don't feel that the 1/4" K.O.s' should be used because of bonding then I would like to know how to make a proper installation.

Curt


Curt Swartz
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
Seems to me that the words " open wiring " in 312.5(B) and 314.17(B) requires single conductor to be firmly secured to the enclosure.

Joined: Oct 2000
Posts: 5,393
S
Member
312.5(B)'s verbage has me picturing those old K&T meters , i am not sure of the definitional interpertation of 'conductor' vs. 'cable' in this article...

314.17(D) here is interesting as i stock #4 cu for all 100 & 200A services....

(D) Conductors 4 AWG or Larger. Installation shall comply with 300.4(F).

which brought me to 300.4(F) here;
Quote

(F) Insulated Fittings. Where raceways containing ungrounded conductors 4 AWG or larger enter a cabinet, box enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place

despite raceway,cable or conductor is the intent of both is 'ungrounded'....?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Apr 2001
Posts: 449
F
Member
The Siemens catalog identifies these as "0.25" K.O." and shows them in the diagram for indoor enclosures(diagram Q7) located in the top and bottom of the enclosure. Why would there be a "weep hole" in an indoor enclosure or a weep hole in the top of any enclosure? In diagram Q2 it refers to these holes as K.O.'s for 0.25" conduit. Since when is there 1/4" conduit? Diagram Q7 also shows 12 K.O.'s for 0.38" conduit. These are all UL listed enclosures.

Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Whoa! I really started somethin'!

Yikes!

[Linked Image]

*runs and hides under bed*


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Boy, I thought my puter was gonna catch fire there for a minute!

[Linked Image]

GWZ,

Splitting hairs with "conductor" vs. "conductors" would be the only loophole out of that one... I think the intent of the NEC would/should be clear, however.

Personally, I wish I could be partially responsible for practically one big black vertical line on the entire '05 code. Just too much subjectivity with the current verbage.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 6 of 9 1 2 3 4 5 6 7 8 9

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5