Is the 1/4" Knock-out hole in the bottom of some 3-R panels and discos an additional "weep" hole (they already have two, one in each corner...) or are they intended for use for the GEC to pass through?
If not, what type of connectors are listed for #6 and #4 bare copper solid soft drawn wire? The NM connectors I buy are only listed for 2 14-2-Gs to 1 10-2-G NM or UF Cables.
I have a feeling I've been doing this wrong for a long time...
[This message has been edited by sparky66wv (edited 09-14-2002).]
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
I have always used the 1/4 knockout fot the #6 ground wire. Was tought that that is why it's there. Never had any inspector say anythig about it. Have worked in 5 different states and at least 15 different cities.
I always thought they were there to be used. They are also in the Bottom and Top of every indoor-rated panelboard that I've ever seen. I've always used them for the GECs.
I thought they were for the flanges (the bolts that hold them on, rather) that fit over the big holes for weather heads. I dunno its always been a guess.
A regional practice in parts of NorCal is the use of 8-, 6- or 4-AWG galvanized/armored bare copper with a 3/8-inch "two screw" connector, and a ground clamp that independently secures/bonds the armor and copper conductor. I believe this has evolved from details in utility-accepted service-entrance requirements.