ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,371 guests, and 52 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 4 of 4 1 2 3 4
#127167 05/18/01 12:05 AM
Joined: Oct 2000
Posts: 4,159
Likes: 5
Member
Just a little trivia here. We had a rep from UL at a meeting and GFCI's was the main topic.

GFCI protection for personnel is set to trip between 4ma and 6ma. An interesting thing mentioned was that the speed with which they operate depends upon the level of the fault. A low threshold 4ma fault could take up to something like 4.8 seconds to trip depending upon the sensitivity of the particular unit.

Bill


Bill
Horizontal Ad
#127168 05/18/01 04:48 PM
Joined: Oct 2000
Posts: 5,393
S
Member
we probably induce more than that doing panel work.... [Linked Image]

#127169 05/18/01 05:41 PM
Joined: Oct 2000
Posts: 4,159
Likes: 5
Member
Another piece of trivia. An Electrical product is permitted to have a loss up to .5ma and still be listed. The importance of this tidbit comes into play where there is a 'nusance' tripping going on. As the GFCI operates on a cumulative value of stray current it could seem to be tripping for no reason but it may be operating perfectly. There could be 8 items on the circuit with a .5 'loss' each (8 x .5 = 4ma) and tripping could occur and there is nothing wrong. It's something to think about when deciding on CB vs Receptacle type GFCIs' and the number of downstream devices and length of a circuit protected by a single GFCI.

[Linked Image]
Bill


Bill
#127170 05/18/01 06:39 PM
Joined: May 2001
Posts: 5
R
Junior Member
If the ground fault was symetrical, it would mean that the human creating the short had three arms of identical impedance. With the current summing at zero in his chest, he wouldn't have cardiac stress, just a real bad feeling in the arms. Quite a party trick.

#127171 05/18/01 07:02 PM
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Bill,

Great point on the line charge Capacitance!!
A great example of when circuit charging becomes a nuisance would be a few extension cords connected together with normal NEMA 5-15 R/P connections, several power tools which use series wound commutator motors with open brushes, and a little bit of rain. This is normally followed by the quick removal of the GFCI breaker, swapped with a standard type frame [Linked Image] [Linked Image]

Another one would be with a whole gang load of cords running everywhere and each being a very long distance [upto 50 feet each], from there many power tools are connected to each cord. Some start and run together, some don't - most have dirty commutators, so the brushes spark like fireworks.
This stuff will trip even the most highest rated GFCI device!!
Long circuits, spark shows on brushes, cords running long distances on concrete/against bonded steel/etc.. many non-coincidental starts/runs on many circuits causes the circuit's charging Capacitance to be really high!

Just FYI. I'll return to my room now [Linked Image]

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 4 of 4 1 2 3 4

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
akmaster
akmaster
alaska
Posts: 75
Joined: June 2012
Top Posters(30 Days)
Popular Topics(Views)
559,091 Are you busy
433,337 Re: Forum
402,197 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5