Thanks all!
Just GeorgeAlthough, were I to nit pick, I would say you should pick either curved or straight; having the left bank elegantly curved and the right side hung up straight in the zip tiesYeah I agree it is kind of strange that I did each side different.
I have to say, I'm a little surprised at the lack of loops in the feedersIt would be rare that I would leave a loop in the feeders. And once you get up above 3/0 CU loops are all but imposable in the space provided.
sierra electrician
Bob, in Pics #1 & #2 you used bond bushings at your service feeders and in Pic #3 a plastic bushing.None of these are services, my normal choice would be plastic bushings.
The customers specifications required the bonding bushings on the side by side panels.
Doesen't the egc have to run continious through the bond bushing to the Gnd bar?It does not have to but that would be the 'normal' way. I so seldom use bonding bushings I forgot to run the EGC through it before cutting it.
So you bagged me on that one.
yaktx
What good does it do to cluster the heavy loads in one place? If you have two large loads on the same stab, doesn't that double the heating on that particular stab?Interesting point, I agree.
I say, run the heavy loads down one side of the panel (say, the left side), and the light loads down the other, or distribute the load in some other way.I have been toying with that in my head as well, I think it makes the most sense electrically but it will look very unconventional.
Maybe I will try that out next time.
I also question the value of perfectly-squared conductors. I've seen too many installers who will commit any atrocity as long as it's outside a panel, but obsess over perfect neatness inside.Another good point, I
could have made these panels neater, but why?
I think we need keep a balance between time spent making the panel obsessively neat and the costs vs benefits to the customer.
My major pet peeve is the abuse of stair-step neutrals. Some installers use up the most accessible lugs first, leaving the service guy to thread wires and screwdrivers through tiny gaps.Boy we really do think alike.
![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
When people use the front first that is just plain ignorant!
Good thinking! This would not have occured to me, although I have certainly drilled into quite a few panels!Thanks
I also have some very short bits for panel work. I keep a 1/4" pilot bit that I intentionally snapped shorter. I can chuck it in my drill with only about 1/4" sticking out of the chuck, it is very hard to get into live stuff with it.
Bob