Joined: Sep 2002
Posts: 947
Likes: 4
N
Member
Classicsat, it is a Cutler-Hammer BR panel,it is too bad they all cannot be that neat, on another note I use very few main breaker panels,and the last one was a SQ D Homeline (yuk [Linked Image] ) and the box was reversable for top or bottom feed, this panels MB operates side to side also, so there would be no reason one could not do so.That would be my only criticism of a fine job.

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Dec 2000
Posts: 4,294
Member
Quote
When I end up troubleshooting on a job like this, yes, I cut the cable ties, but I replace them afterwards,

Funny, I do just the opposite [Linked Image]
I make up new panels using ty-raps, and then when I'm done, I cut them off. Conductors bundled over 24" require derating.

This is a beautiful job !!

Joined: Dec 2004
Posts: 329
I
Member
Very sharp work. You get a gold star.
Working on military sytems, this is the way that it is supposed/required to be done. That said, many of our techs dont even do this nice of a job.
Be proud.

Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
Conductors bundled over 24" require derating.

Not in a panel. [Linked Image]

Derating only applies to raceways or cables.

That aside I do not generally tie wrap in panels either.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Mar 2001
Posts: 2,056
R
Member
Classicsat,

I thought sub-panel at first, but the bonding strap hasn't been removed and the neutral buss is bonded via the green screw and copper jumper.
Apparently it is simply for neatness and it looks good.

Joined: Jul 2003
Posts: 394
B
Member
Note to renosteinke: Please notice I made no comments about the listing on the clamps. There are no faults with respect to code compliance. There are variations in style and I just compared it to mine. Food for thought, so to speak.

Joined: Mar 2005
Posts: 34
C
Member
Where is the green bonding screw?

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Mar 2001
Posts: 2,056
R
Member
The bonding screw is just above the 5th branch circuit conductor on the right side, just to right of the neutral bundle.

Joined: Nov 2000
Posts: 246
R
Member
One other thought, other than praise. Does this seperation of the phase conductors and the neutral cause increased EMFs? If it does, is it enough to cause concern?

I seem to remember a class by Mike Holt about this.

Looks great tho!

Rick Miell

[This message has been edited by rmiell (edited 11-14-2005).]

Joined: Aug 2003
Posts: 64
E
Member
Redsy,

Quote
I thought sub-panel at first, but the bonding strap hasn't been removed and the neutral buss is bonded via the green screw and copper jumper.
Apparently it is simply for neatness and it looks good

Another piece of evidence would be what appears to be a GEC entering the bottom left of the enclosure and landing on the ground bar.

Page 3 of 4 1 2 3 4