|
|
|
0 members (),
119
guests, and
14
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Jul 2002
Posts: 8,450 Likes: 4
Member
|
Wow!, This looks like a big job. Just a silly little question, were the wires in the 3 conduits above the one that blew out, checked or tested to make sure that they weren't damaged from the heat?. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
OP
Moderator
|
Hi Mike were the wires in the 3 conduits above the one that blew out, checked or tested to make sure that they weren't damaged from the heat?. All wires replaced. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) The switchgear was checked by a manufacturers (GE) technician. Bob [This message has been edited by iwire (edited 12-27-2004).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Jun 2004
Posts: 206
Member
|
Mike, not a silly question at all. As Bob said all cables were replaced. Yes it was a big job. We started out with five guys at 6AM. Brought in 2 more at 10AM, and 3 more at 4PM. We all left at midnight with everything packed up. Except for the painters coming the next day you would never have known we were there.
|
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I'll take a stab at the cause: Insulation damage on the conductors in the bottom conduit where they emerge through the bushing.
It looks like the bonding-bushing lugss on the other three conduits could be pressed into their respective conductors, too.
I try to "pre-bend" wires to keep them centered in, or at least not jammed against, the conduits from which they emerge.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
I say it was the bullet hole in the conduit in picture #3. What ever blew it was vaporized early in sceme of things.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
Bump... ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
Stupid should be painful.
|
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
Now THAT is a real eye opener to what can happen !!!That would have been something pretty spectacular to see... That would put some fireworks displays to shame!
Some years ago when I used to work at the supplier a building down the road had its main underground service short out and it also wiped out the padmount transformer ( Service was 400A 120/240V 1 phase, that consisted of 2 ducts containing 3/0 TWH in paralell)... One of the ducts shorted and burned the conductors bare from the transformer to the fault... Turns out when they were pulling out the damaged conductors, a chunk of broken fish tape was drawn out right where the fault appeared to have originated, and had been tangled in there since day one.. About 15 years if not a bit longer..
A.D
|
|
|
|
|
Joined: May 2015
Posts: 1
New Member
|
Bob, Could I have your permission to use your photo. Of course I would give credit.
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 9
Member
|
DHester: Welcome to ECN forums!
Iwire (Bob) has not been active on this forum for some time.
You may want to try sending him an email.
John
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|
|
|