Bob,I also stand by mine
645(D)...."shall be permitted under a raised floor, provided the following conditions are met."
(2) "The branch-circuit supply conductors to receptacles or field-wired equipment are in rigid, metal conduit, rigid nonmetallic conduit, intermediate metal conduit, electrical metallic tubing, metal wireway, surface metal raceway with metal cover, nonmetallic surface raceway, flexible metal conduit,
liquidtight flexible metal conduit, or liquidtight flexible nonmetallic conduit, Type MI cable, Type MC cable, or Type AC cable.
These conductors shall be installed in accordance with the requirements of 300.11"
"
300.11 Securing and Supporting
(A) Secured in Place. Raceways, cable assemblies, boxes, cabinets and fittings shall be securely fastened in place"........
If that were the case, all of 645(D)(2) would be for nothing.
Do you agree that it's just sealtite and boxes field assembled?
Under your reasoning, could I run EMT without securing it?
Glad to see we're back to our "normal" selves
I was fearing we'd begin to agree on
everything