[Linked Image]
Quote
Here's a panel in a house only 3 years old. Note the conductors around the buss bolts, they come from the generator disco which is NOT a DPDT, only a DPST, and it feeds the whole panel... Not clearly visible are six single pole 30A breakers feeding the #12 and #14 receptacles and lights feeders.

He wanted me to put an indicator light in before the main so he could tell when the power came back on...

-Virgil

Horizontal Ad
#112505 06/30/01 06:40 AM
Joined: Oct 2000
Posts: 5,393
S
Member
there is no noodle isolation here either, given a main disco before this panel.

maybe the indicator light needs to be @ the firehouse?

[Linked Image]

#112506 06/30/01 08:35 AM
Joined: Dec 2000
Posts: 4,294
Member
You've sure got the haywired customers, Virgil. Did this guy explain to you his sequence of breaker flipping-switch throwing in the event of an outage? Oops would sure cause him some trouble. I think he'd be better off with a Maglite and some Coleman lanterns.

#112507 06/30/01 05:47 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
There was a homemade set of instructions on the panel cover with lots of !!!! explaining the procedure. There was a 30A 240V (not 120/240V) disco for the genny above the panel. He didn't understand when I tried to explain that the feeders between the 30A disco and the panel were hot and "protected" at 200A, only #10 wire with very bad connections... No box in the house was bonded, grounds twisted together with no connector, boxes way too small (those 45ยบ angle corner metal boxes), etc. etc. on and on... (boy I sound like a scratched record sometimes...)

He refused the work and said he'd take care of the 30A breakers himself.

How much you want to bet that they would trip 15's anyway do to overload.

How 'bout I change the subject before I become depressed?

Steve,
No main disco (back to back, kinda) so the neutral is OK...

[This message has been edited by sparky66wv (edited 06-30-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,925 Are you busy
254,755 Re: Forum
237,179 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5