Sven:
Brian is correct once again.  If I understand what you mean by 2-pin surface mount sockets (Leviton's Lev-O-Lets, for one example), you're talking a completely different animal.  I don't believe any manufacturer has the requirements for such devices that would justify automation.  So, for those and for 3-pin surface mounts, you're talking more parts and labor for the grounded.
A corporate type once asked me, with some annoyance, why isolated grounding makes for more expensive devices in commercial duplex receptacles but less expensive devices in power receptacles.  Similar answer: different construction.  In the crowded and busy guts of a standard-size duplex, we have to work harder.  One solution is an insulator that sits against the metal strap, separating the ground contacts from the strap, and terminating in either a ground lead or a lug with a ground screw.  By contrast, in a power receptacle that is mostly plastic body against metal strap, to even achieve a ground we have to add a shunt to the ground contact and rivet the shunt to the metal strap.  Want the ground isolated?  Leave out the shunt and rivet, and the attendant labor and overhead.