This is a C.T. cabinet and the electrician decided to use some old terminal lugs instead of splice blocks to connect the wires and save some money. It looked neat and I almost approved it until I studied it further because something just didn't look right. Gut feeling or instinct. Then it dawned on me. The lugs were screwed to the plywood backboard with long wood screws. Long enough to penetrate all the way through the wood to the metal cabinet. If I had allowed it to be energized it would have flashed over behind the wood. (Note; The local utility requires the wood backboard. I don't like it but, can't make them change.)
Alan Nadon ![[Linked Image]](https://www.electrical-contractor.net/Forum/Images/CT_Cabinet.jpg)
|
|
|
|
|
Joined: Feb 2006
Posts: 144
Member
|
The utility *requires* this?!? That seems rather odd.
|
|
|
|
|
Joined: Dec 2005
Posts: 873 Likes: 4
Member
|
Strange that the utility allowes the extra fire danger. In NZ the CT cabinets are from steel, The bussections or blocks are mounted on insulated stand offs. A PVC cover is fitted to cover the exposed bare copper terminals, underneath the CT chamber door to avoid direct touch contact to exposed live conductors.
The product of rotation, excitation and flux produces electricty.
|
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
Utility requires the wood back to make it easier for them to mount different size current transformers. Listed CT enclosures are required to provide adjustable mounting brakets and to pass an ice test. This cabinet and others like it are listed only as junction boxes, not CT enclosures. For years the utility supplied them and they were utility property. Now with deregulation the contractor has to supply them but, this is the only style they will accept. They have worked for years and I don't feel up to a fight with the utility company. ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif) Alan-- As Kenny Rogers sings: "Sometimes you hold 'em, sometimes you fold 'em, sometimes you walk away..."
Alan-- If it was easy, anyone could do it.
|
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
I am not an electrician, but I have an interest in becoming one.
Why is there such a difference in the wire sizes for the incoming service and the load?
LarryC
|
|
|
|
|
Joined: Nov 2001
Posts: 745
Member
|
The wood screws for the lugs not withstanding, it looks like the two hot legs are double-lugged.
Isn't some type of bonding supposed to take place in here?
I may be missing something obvious, but which side is line and load?
Mike (mamills)
|
|
|
|
|
Joined: May 2005
Posts: 178
Member
|
Mike, I think if you look closely, it's not double-lugged. The center wire has its own hole, right in the middle and underneath the other two. The middle setscrew is to the right of the others.
I'm not sure, but I think I see the enclosure bond at the bottom left. Either that, or the EGC is just lying loose! The conduits are probably RNC, so no bonding nuts.
I'll guess that the larger wires are the load, that they've been beefed up to reduce voltage drop on a long run, and that they go to two separate load centers. (Am I close?)
Alan, suppose those lugs had been bolted to a separate plate of plywood, then screwed as an assembly to the backboard. There'd be a full thickness of plywood between live parts and the enclosure. Would you have accepted it then?
|
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
Alan, suppose those lugs had been bolted to a separate plate of plywood, then screwed as an assembly to the backboard. There'd be a full thickness of plywood between live parts and the enclosure. Would you have accepted it then? Don't know for sure how Alan would feel, but I would not. It would still be possible, given enough moisture buildup in or on the plywood to form a conductive path, with heating, arcing or a flashover possible. Painting the wood won't help either as some paint is at least semiconductive. edited to fix a missing word.. [This message has been edited by mxslick (edited 07-15-2006).]
Stupid should be painful.
|
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
LarryC: Electricain has to size wire to the NEC. Utility co sizes their wire to expected load. If their wire fails they replace it. Until then they save money. John: You're right all the lugs had three openings. Conductor with green tape is a bond and then goes to the ground rod. Although the six screws through the plywood on the grounded phase made an effective bond although unintended. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) Conduits are non-metallic. If I remember right parallel conductors went to a single panel, located just inside the wall. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
Does the utility in question require fire treated plywood for these improvised CT cabinets. There is a very nice insulated lug made by Polaris Connectors that would be perfect for that application. http://www.polarisconnectors.com/37022_POLSAL_EXTRA_IPLMD1.pdf It has insulated mounting holes in each end to hold it in place. Is that what you meant by the term splice blocks? -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison [This message has been edited by tdhorne (edited 07-16-2006).]
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
|
|
|
|