Page 2 of 2 1 2
#108760 11/19/03 01:33 AM
Joined: Jun 2003
Posts: 681
P
Member
How about pipe fill, and bending radius? I cannot see how either can be complied with.

Pierre


Pierre Belarge
Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

#108761 11/19/03 07:34 AM
Joined: Oct 2000
Posts: 5,393
S
Member
a valid Q GETELECTRIC...

what is the dif bettween this raceway , amd all the wells out there running conductors in wellpipe?

myself, i don't go off on a rating/listing jingle anymore, i simply tell people that a raceway should identify itself as to it's contents...

#108762 11/19/03 09:15 AM
Joined: Dec 2000
Posts: 4,294
Member
There's a product made for copper that's a "cold solder", made for repair work. It doesn't require a torch.
None of the plumbers I know would ever use the stuff, but it's just possible that that's what was used to get that 90 on...S

#108763 11/19/03 12:49 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Instead of the "water pipe", wouldn't a reasonable solution be containing UF romex in {notched} wood molding up the side of the pole?

#108764 11/27/03 12:56 AM
Joined: Jul 2003
Posts: 141
S
Member
According to the NEC, 3/4" conduit can't have a radius tighter than 4 1/2 inches using one shot or full shoe benders, and "other bends" can't be tighter than 5 inches. See NEC 358.24 and table 344.24.

#108765 11/27/03 01:02 AM
Joined: Jul 2003
Posts: 141
S
Member
And another thing. According to 358.6, it says "EMT, factory elbows, and associated fittings shall be listed." I doubt if copper tubing with sharp 90s would be considered listed for that use.

Also, according to 358.2, it says "EMT is generally made of steel (ferrous) with protective coatings or aluminum (nonferrous)." It doesn't say copper can't be used in that article.

#108766 11/27/03 02:03 PM
Joined: Oct 2003
Posts: 172
G
Member
shame to anyone who would chastise this work going by what we see in the picture. those of you who haven,t done anything that compares to this interms of code violation are either full of s... or have an halo for a hard hat.

Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

#108767 02/24/04 02:17 AM
Joined: Feb 2004
Posts: 1,440
Member
In this installation, I probably would've gone with schedule 80 & a PVC LB(sunlight resistant) for resistance to the elements & possible impace damage... As for aesthetics... A simple coat of spray paint before installation to match the pole [Linked Image]

#108768 02/26/04 08:54 PM
Joined: Aug 2003
Posts: 31
M
Member
Could these lamps be low voltage?