0 members (),
1,163
guests, and
24
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
The male end of a cordset was cut off going into this panel. I suspect a generator was used to feed the lower left 2 pole breaker since the black is stripped twice and isn't long enough to reach much else. Also found several breakers and neut's double lugged. Not a big deal but I thought it was kind of funny KentVW ![[Linked Image]](https://www.electrical-contractor.net/forum/el/kent.jpg)
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I consider this a big deal, I have a real problem with people that back feed panels with a generator.
Ask anyone of these people and they will tell you that they will never make a mistake and they will always turn off the service disconnect while they have the generator on line.
Well we are all human and make mistakes, a mistake made here may injury or kill a lineman while they are trying to fix the outage.
Well enough venting, Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Feb 2004
Posts: 4
Junior Member
|
Before we assume that was a backfeed- I must make a comment. I have somthing similar on my own panel in the basement, and what I do is when the power goes out, I pop the panel cover and connest the cords wires to my furnace, since it is the only appliance that I need that isn't cord-and-plug connected.
|
|
|
|
|
Joined: Feb 2004
Posts: 1,440
Member
|
this kinda looks like a subpanel, with grounds on the neutral bars.... Nice cord grip by the way! ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif) Also, backfeeding both phases on one phase can allow shared neutrals to be overheated.. (Not that the extension cord here could carry enough current to do that though..) -Randy
|
|
|
|
|
Joined: Mar 2004
Posts: 391
Member
|
And to boot, I'm pretty sure that weather-proof receptacle cover is mounted sideways, the drip edge is now perpendicular to the earth... Could be a violation of 110.3(B).
-John
|
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
I've got to agree ( ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif) ) with Bob. A panel backfed this way is a big time hazard to linemen. ...S
|
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
If it is fed 110V to _both_ legs of the panel, then it doesn't present the high voltage hazard usually connected to a backfed panel...the voltage across the transformer secondary would be 0V.... Still ugly and a safety hazard, and I don't intend to defend this practise ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif) -Jon
|
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
As electricians, we may not agree 100% with what utilities require, but with a clear understanding of the very serious hazard backfeed can create for lineworkers, we should firmly support the prohibition of everything that has the potential of creating such a situation.
This means nothing but professionally installed, listed, lockable, externally-operable, visible-blade, center-off double-throw disconnect switches at the building meter location, and clearly rejecting any tin-can-grade breaker-handle “interlocks” intended for non-utility alternate-power sources.
[Backfeed attempts are also a top-flight way to fry generator sets.]
|
|
|
Posts: 349
Joined: April 2004
|
|
|
|